I agree, and maybe even argue it would be OK on a B20 MCB (subject to max Zs and voltage drop being OK). I like creative circuits that don't follow the expected norm!
I dont, this just demonstrate's lack of knowledge/adhering to basic craft principles that we are all taught in circuit design, far too much of this do as you likey attitude trying to be smart, and its shows with the amount of questions/ query's that get posted on here trying to find a work around.
 
Is there any sign of thermal degradation? What was the IR like for the both ring circuits? Also what kind of loads were observed in use? C2 could be argued with as the question is what is the likely danger in the future that may present itself? C3 is reasonable as it points to a safety upgrade which I would think is fair enough. So when we do an EICR what is the purpose, to state whether the installation is safe for continued use. As it is then a C3 and no more with explanation. If anything does happen than at least you have brought it to the attention of the person ordering the work.
 
Aubergine?
I will skip the emoticon for obvious reasons :)
[automerge]1598122988[/automerge]
Back to the OP, it is unusual as you say but not unsafe. My own flat was on a 20A rewirable (originally, then MCB) for the RFC but sensible enough of 2.5mm T&E and never had issues of tripping without 13A fuses blow. C3 folks?

The argument about it being modified to be unsafe by changing to 32A MCB is a bit dubious as anyone doing that ought to be covered by Part P regulations (I guess, not in my backward/forward region) and they damn well should know better!
Regardless of any alteration being subjected to Part P, and you are correct, but how many of todays DIYers will bother with part P? " please come and mend my electrics", "" 20 quid love OK"" we all know that many will just swap the OCPD as a matter of keeping the power on an booger Part P. my argument still stands, as far as I'm concerned.
 
Last edited:
Don't often disagree with you Mate, but on this I do, although the cable as you say is good for 19Amps on a 16 A breaker should be OK, what would happen if there is a lot of nuisance tripping, due to people overloading the 16 Amp OCPD and someone decided to up the OCPD to a32 Amp OCPD, sorry to be at odds with someone I admire but in this case I think you are wrong, change to a 20 A radial or 32 A RFC wired in N 2.5mm2 cable

But what if someone changes those MCB's you are recommding for a larger one?
Regardless of any alteration being subjected to Part P, and you are correct, but how many of todays DIYers will bother with part P? " please come and mend my electrics", "" 20 quid love OK"" we all know that many will just swap the OCPD as a matter of keeping the power on an booger Part P. my argument still stands, as far as I'm concerned.

That can be said about any part of the electrical installation.
They could do exactly the same with any other MCB.

Every part of the installation could/might be altered incorrectly so woukd you just code the whole thing?
 

Reply to Coding for a Ring Final Circuit 1.5/1mm in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock