- May 26, 2020
- 23
- 21
- 33
- United Kingdom
Afternoon all,
A quick EICR question. I have found a Ring Final Circuit that has been run in 1.5/1mm twin and earth. It is RCD protected and OCPD is a 16a type B MCB. All testing has come back as expected for a Ring final that has been installed in 1.5/1mm and the measured Zs is well within max values. The installation actually has an EIC and has been recorded as being installed in 1.5 method C.
Im not sure on coding, could arguably be C2 as it is not able to be considered a RFC in accordance with 433.1. Could be C3 as although not an approved method it’s not dangerous and the cable is protected by the OCPD. Could even arguably be no code for the same reasons as reduced conductor size is allowed for socket outlets elsewhere.
I’m torn between a C3 and C2 citing 433.1.
If coded as a C2 and asked to complete remedial works, would you consider removing one leg of the ring and have the circuit as a 16a radial, but in my opinion this does not really change the safety of the installation and still isn’t best practice due to the cable sizing?
- TL;DR
- Coding for a Ring final in 1.5/1mm T&E