I havent done an ir test yet i wanted to narrow it down before i start charging. Its been happening on and off for a couple of months. But as i described it could be either of the rcd's or both at the same time.

For goodness sake man, you are supposed to be a professional electrician are you not? Charge an appropriate callout for the first hour you are there and an hourly rate after that. Having a look, narrowing down, asking a forum, etc etc is hardly the work of a professional is it? I dread to think what your customer must think of you!

Why would you not carry out an IR test when you have the clear symptoms of a very common fault, namely a N-E fault.,
 
Thanks for the advice guys i think this one is going to be a thorough investigation of every circuit to find the cause.
 
As above Paul I would definitely be doing an IR test between N-E to start off with. Asking questions as you are doing would be more suited to asking the client as they will be able to perhaps give you some clues (i.e time of day, heavy rain, when an appliance is switched on etc) whereas we would just be guessing. It's a bit like saying to a mechanic 'my cars broken down could you tell me whats wrong please'. The thread below is just one of many on the forum that talks about fault finding tripping RCD's.

http://www.electriciansforums.co.uk...ical-forum/64088-rcd-tripping.html#post640772

Here is a PDF about tripping RCD's that is quite interesting as well.

View attachment understanding RCD's and tripping problems..pdf

In addition 'I think' Richard Burns has talked in a post (and drawn some good diagrams) about the 'opposite' RCD tripping. I.e a circuit on the right of the board making the RCD on the left trip. I can't quite get my head around this as there shouldn't be an imbalance. Anyway, that's digressing and I think you should start at the beginning with your N-E tests!
 
As above Paul I would definitely be doing an IR test between N-E to start off with. Asking questions as you are doing would be more suited to asking the client as they will be able to perhaps give you some clues (i.e time of day, heavy rain, when an appliance is switched on etc) whereas we would just be guessing. It's a bit like saying to a mechanic 'my cars broken down could you tell me whats wrong please'. The thread below is just one of many on the forum that talks about fault finding tripping RCD's.

http://www.electriciansforums.co.uk...ical-forum/64088-rcd-tripping.html#post640772

Here is a PDF about tripping RCD's that is quite interesting as well.

View attachment 32176

In addition 'I think' Richard Burns has talked in a post (and drawn some good diagrams) about the 'opposite' RCD tripping. I.e a circuit on the right of the board making the RCD on the left trip. I can't quite get my head around this as there shouldn't be an imbalance. Anyway, that's digressing and I think you should start at the beginning with your N-E tests!

Why just the N-E tests? When doing IR tests you need to do them all and in a logical manner
 
Why just the N-E tests? When doing IR tests you need to do them all and in a logical manner

That's what I tend to start with Murdoch, that usually shows up the faulty circuit, but then if still no luck then the earth clamp meter comes out.
 
In addition 'I think' Richard Burns has talked in a post (and drawn some good diagrams) about the 'opposite' RCD tripping. I.e a circuit on the right of the board making the RCD on the left trip. I can't quite get my head around this as there shouldn't be an imbalance. Anyway, that's digressing and I think you should start at the beginning with your N-E tests!
I hope I have not provided unclear information.
One key thing to remember is that (barring irregular voltage transients) if an RCD or RCBO trips then the fault must be on the circuit(s) that the RCD is protecting, the fault cannot be on a circuit not connected to the RCD.

However for a neutral earth fault present on a circuit protected by the RCD, a load on a circuit not protected by the RCD can allow diverted current to flow through the NE fault on the faulty circuit and trip that RCD, however the fault is on the circuit protected by the RCD, not on the circuit that appeared to cause the RCD trip.
RCD Trip due to other side loading.jpg
 