- Reaction score
- 7,784
micc on rcbo will not set
Discuss micc on rcbo in the UK Electrical Forum area at ElectriciansForums.net
When you swapped from RCBE to MCB is there a chance you could take an earth leakage reading, that may throw some light on the problem, as the problem is pointing to a leakage fault somewhere.yes pete999 tested line to earth >999 neutral to earth >999
I am asking if the neutral core is connected to the RCBO and not to the neutral bar, as if you have been swapping back and forth MCB to RCBO this could get missed.
If the light fittings are class II then there cannot be an earth fault there so there must be something else causing the problem.
Used MICC in Council new build flats in the 60s (1960s for the comedians out there)
Dark art that Pete.Used MICC in Council new build flats in the 60s (1960s for the comedians out there)
when back to day to look at the job.on to test the micc the reading went mental on IR
looked at the bathroom enclosed light the bowl was full of water & the base
the only thing was missing a gold fish . found out the flat above had a leek
went to the flat below
Dot comNow I'm really confused!
I think hightower has probably got it spot on there. Daz
Must agree the IR must have been low anyway, init.So the RCBO was doing the job it was designed for I wondow how long the MCB would of held before it went bang!
Surprised that the IR test didnt reveal leakage I am surpised re the readings (IR)that were posted!
Thanks for the translation Hightower !!!
That's why I was confused at #49.Must agree the IR must have been low anyway, init.
How right you areBuzz is alarming.
Reply to micc on rcbo in the UK Electrical Forum area at ElectriciansForums.net