Not yet but registered with LABC as a competant person
Cool how does that work? Interested cos I'm paying 500 squids to Elecsa

Not yet but registered with LABC as a competant person

Ive had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a schemeCool how does that work? Interested cos I'm paying 500 squids to Elecsa![]()
Ive had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a scheme

explain to customer about the TT system & you strongly recommend to bond the water if Metal incoming or even plastic before I get my head bitten off, check readings first if plastic to see if it needs bonding.
gas bonding or oil if they have it.
explain these will need to be done before you can do any electrical work on the bathroom.
install 100ma trip s type on mains & new earth rod or alternatively if readings are good & you can bond water & gas install a 16mm tail from consumer unit into a MET block ring up board & ask for an earth upgrade to PME.
normally free of charge I have done this years ago for customer but check readings first mainly ZE.
if not then go with new rod bonding & 100ma trip before you start the bathroom.
also so you don't have to test the whole house if you can run a new circuit for bathroom lights & install on own RCD unit then do this & issue an electrical certificate for your works.
Sent my quals off to LABC got a letter back asking if I was any good at road sweepingIve had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a scheme
Not wishing to dis some of your advice, but struggling a tad with some.
Metal services must be bonded. Plastic services do not need bonding, and wouldn't waste my time checking them. The metal pipe work that runs from the plastic services may need bonding (528.3).
Changing from TT to TN-C-S may have a cost implication to the client which may not be necessary (although I would), and I wonder why installing 100mA S Type in this situation, would be a consideration. And OP doesn't have to test the whole installation, if he is doing an alteration or addition (minor works).
I'm always learning, so I willing to stand corrected.
Parrallel paths?Still would like to know why Ze changed when you disconnected water bonding.
My original ze test was with main bonding and main earth both connected in the MET and a reading of around 4ohms obtained. I then removed the main bonding to the incoming water performed a ze test again and got a reading of 20ohmsIf you did not disconnect the main earth from the MET you would have the water pipe as parrallel earth causing a misleading Ze reading
Thats very naughty thenwater bond is probably providing the earth
YesSo that second reading is your Ze which is ok then.