Cool how does that work? Interested cos I'm paying 500 squids to Elecsa :mad:
Ive had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a scheme
 
Ive had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a scheme

Not such thing then, as a free lunch. You might wanna try Stroma at £285 (I think), although their on-line software is pants (so I'm told) :rolleyes:
 
explain to customer about the TT system & you strongly recommend to bond the water if Metal incoming or even plastic before I get my head bitten off, check readings first if plastic to see if it needs bonding.
gas bonding or oil if they have it.
explain these will need to be done before you can do any electrical work on the bathroom.
install 100ma trip s type on mains & new earth rod or alternatively if readings are good & you can bond water & gas install a 16mm tail from consumer unit into a MET block ring up board & ask for an earth upgrade to PME.
normally free of charge I have done this years ago for customer but check readings first mainly ZE.
if not then go with new rod bonding & 100ma trip before you start the bathroom.
also so you don't have to test the whole house if you can run a new circuit for bathroom lights & install on own RCD unit then do this & issue an electrical certificate for your works.

Not wishing to dis some of your advice, but struggling a tad with some.

Metal services must be bonded. Plastic services do not need bonding, and wouldn't waste my time checking them. The metal pipe work that runs from the plastic services may need bonding (528.3).

Changing from TT to TN-C-S may have a cost implication to the client which may not be necessary (although I would), and I wonder why installing 100mA S Type in this situation, would be a consideration. And OP doesn't have to test the whole installation, if he is doing an alteration or addition (minor works).

I'm always learning, so I willing to stand corrected.
 
Ive had to send off copies of my relevant certs, 17th edition and 2391 inspection and testing. Once theyre satisifed with these i go on there register. Problem is every time i do any work that is notifiable i have to fill in a building notice form and send it off to them along with a fee of £82. The fee is payable for every notifiable job i do so being in a scheme is probably more cost effective long term. I just didnt want to lose out on any potential work in the short time whilst im not registered with a scheme
Sent my quals off to LABC got a letter back asking if I was any good at road sweeping:cry:
 
Not wishing to dis some of your advice, but struggling a tad with some.

Metal services must be bonded. Plastic services do not need bonding, and wouldn't waste my time checking them. The metal pipe work that runs from the plastic services may need bonding (528.3).

Changing from TT to TN-C-S may have a cost implication to the client which may not be necessary (although I would), and I wonder why installing 100mA S Type in this situation, would be a consideration. And OP doesn't have to test the whole installation, if he is doing an alteration or addition (minor works).

I'm always learning, so I willing to stand corrected.

might have read slightly wrong with plastic pipe & not mentioning the metal part after.

changing from TT to PME or TN-C-S has always been free for me & have done quite a few

the 100ma trip S type is normally used to protect cabling in the infrastructure more important in what was 16th edition as lights ect did not require RCD protection now most circuits are 30ma protected. but I would always do a TT system with 100ma trip & the reason for s is the time delay so the 30ma will trip first if you only use 100ma without S type they can go at the same time as the 30ma & take out whole board.
me now with metal clad board cables in there unprotected I would install the 100ma trip on a TT.

testing meaning the one circuit or more if pumped shower (running of sockets) & lights running of lighting, i would want to test the whole circuit before i put an RCD at the mains hence the mention of RCD spur above the door & protecting just the work i would be installing so i don't have to test the whole circuit.
 
It might be just the way your wording your replies then.

I have never been involved with costing of conversions to PME, but I've read of different responses by DNO's with regarding to charges, something to consider before going ahead with it perhaps.

Agree with you re 100mA S Type on TT supplies and A3 CU's, the OSG gives some suggestions for all supplies (3.6.3.3). There are other considerations for TT, distribution circuits for example.

Still not clear what you mean in your last paragraph. Installing a local RCD, would still need the series of tests conducted for the whole circuit, not just the piece after the RCD.
 
If you did not disconnect the main earth from the MET you would have the water pipe as parrallel earth causing a misleading Ze reading
 
Typical TT the water bond is probably providing the earth and the connection to the electrode is probably doing no more than earthing it.
 
If you did not disconnect the main earth from the MET you would have the water pipe as parrallel earth causing a misleading Ze reading
My original ze test was with main bonding and main earth both connected in the MET and a reading of around 4ohms obtained. I then removed the main bonding to the incoming water performed a ze test again and got a reading of 20ohms
 
So that second reading is your Ze which is ok then. I think that might be a bit of a poser then bacause the water sounds like a better earth than the main earth so it would then act as earth in fault conditions....hmmmmm
 