So that second reading is your Ze which is ok then.
Yes
and a reading of around 4ohms obtainedMy original ze test was with main bonding and main earth both connected in the MET. I then removed the main bonding to the incoming water performed a ze test again and got a reading of 20ohms
Leep82,you keep stating that you measure at the met at a time with bonds connected then disconnected
Has a loop reading been taken off the assumed 10mm cable with it actually disconnected from the consumer unit?
It seems to my reading that a Ze has always included parallel paths on each occasion if that reading has been taken at the met,it seems no assurance of any kind of electrode connection has been carried out