So that second reading is your Ze which is ok then.
Yes

and a reading of around 4ohms obtainedMy original ze test was with main bonding and main earth both connected in the MET. I then removed the main bonding to the incoming water performed a ze test again and got a reading of 20ohms

Leep82,you keep stating that you measure at the met at a time with bonds connected then disconnected

Has a loop reading been taken off the assumed 10mm cable with it actually disconnected from the consumer unit?

It seems to my reading that a Ze has always included parallel paths on each occasion if that reading has been taken at the met,it seems no assurance of any kind of electrode connection has been carried out
 
Leep82,you keep stating that you measure at the met at a time with bonds connected then disconnected

Has a loop reading been taken off the assumed 10mm cable with it actually disconnected from the consumer unit?

It seems to my reading that a Ze has always included parallel paths on each occasion if that reading has been taken at the met,it seems no assurance of any kind of electrode connection has been carried out
No I havnt disconnected the assumed main earth from the MET to do a Ze only the known main bond to the water. I assumed with the main bond disconnected it would in essence be a true Ze reading, what other parrallel paths could there be? The c.p.c's for the connected circuits were also in the MET at time of test. Should i have actually disconnected the assumed main earth form the MET and done a Ze test that way?
 
You should disconnect it to be absolutely sure there are no parallel paths. Could be supplementary bonding for example which could bring the water pipe into play through some convoluted path.

I'd also be inclined to double check that the other 10mm isn't actually connected to the gas pipe. I did a job the other day two 10mm bonds, one traced to water, the other to the gas (verified by continuity) but the clamp was nowhere to be found and the cable just disappeared off somewhere.
 
Should i have actually disconnected the assumed main earth form the MET
Well really this is what I was sneakily alluding to without wishing to cause concern. So you are measuring external E ohms hence mains off and Main E disconnected from MET so you can only be measuring Ze. But clearly if its one of them MET on the board outside the DB then you can see there is nothing connected to it, it is the same really.
 
You should disconnect it to be absolutely sure there are no parallel paths. Could be supplementary bonding for example which could bring the water pipe into play through some convoluted path.

I'd also be inclined to double check that the other 10mm isn't actually connected to the gas pipe. I did a job the other day two 10mm bonds, one traced to water, the other to the gas (verified by continuity) but the clamp was nowhere to be found and the cable just disappeared off somewhere.
There is definately no bond to the gas. The gas supply is visible its entire length on the outside of the building from the meter at the front
You should disconnect it to be absolutely sure there are no parallel paths. Could be supplementary bonding for example which could bring the water pipe into play through some convoluted path.

I'd also be inclined to double check that the other 10mm isn't actually connected to the gas pipe. I did a job the other day two 10mm bonds, one traced to water, the other to the gas (verified by continuity) but the clamp was nowhere to be found and the cable just disappeared off somewhere.
There is definately no bond to the gas. The gas supply runs externally down the side of the house and is visable for its entire run. It enters the property at two points the boiler and the gas hob. I checked at both points and no bonding present. I also checked in the meter enclosure before anyone asks
 
So that second reading is your Ze which is ok then. I think that might be a bit of a poser then bacause the water sounds like a better earth than the main earth so it would then act as earth in fault conditions....hmmmmm
This is par for the course on TT systems with metal piped services bond the gas, assuming a metal service pipe the Ze will probably be even lower.
 