Pulling the dno fuse | Page 2 | on ElectriciansForums

Discuss Pulling the dno fuse in the UK Electrical Forum area at ElectriciansForums.net

Joined
Aug 20, 2017
Messages
12
Reaction score
6
Location
Sleaford
Hi all

The other day a friend of mine who owns a restaurant lost power so I went to take a look for him as I was only around the corner. Upon arriving I found that the tails straight off the meter into the switch fuse had burnt out and one of them was hanging out the box (it was quite a mess and I took photos). As i didnt have any tools on me at this point i couldnt check to see if the cables were safe (although I suspected it had blown the main fuses) so I pulled the main fuses (I didn't cut any tags) as this was the only means of isolation. I then called the electric board to come out and went to fetch my van to take a closer look.

When the man came out he gave me a lot of ---- and wanted to report me saying I put myself in huge danger (in the end he calmed down and said he wouldnt) but Its been playing on my mind. I was well aware of the risks of pulling the fuse but I thought there was a greater risk of leaving it and in the hour the at they took to come out what if i had my back turned and a member of the public had walked in and touched something.

Was he right in saying that I should have just left it because as far as I believe, if something was to have happened they would have said it was the electricians responcibily as it wasn't on their side of the meter. Do you think I did the right thing or could I have handled it any better?
 
As there was an immediate risk to life through a potential fire risk I would have done the same thing.

If the DNO wanted to take it further, crack on and see you in court.
That's what I thought, I was just seeing what other people would have done in this situation as I have not come across this before. I thought the way the technician acted was really unprofessional as he was shouting at me in front of the client saying i didn't know what I was doing. Even if he wasn't happy with the way I did things he could have pulled me to the side and had a chat with me. Luckily in this case the client was a friend
 
We all can act out of turn, when faced with a stressful situation. I guess that's why the DNO engineer lost his cool slightly. I suspect, given the opportunity, he would have commended you for your actions, but would of calmly explained the dangers of what you did.

Seems you acted in good faith, and for the benefit of others. Having had time to reconsider, would you do the same again?
 
I have withdrawn the DNO fuse in the past, the reason was the meter was smoking and arcing, I contacted the DNO for an emergency attendance and got he usual rhetoric on the phone about withdrawing the fuse and that it is illegal to interfere with their property, after telling them the reason their attitude quickly changed and it wasn't taken any further.

Having said this though, even in said situation there can be some big risks in doing so, especially if the cutout is damaged or aged, I have seen DNO cutout installers/upgraders on a few occasions refuse to touch the cutouts until power is removed upstream, when even the DNO won't pull the fuse live, you have to realise that the consequences can be deadly especially if you are ignorant to the possible risks.
 
As several others have already said, and in my opinion, you did the right thing and I would have done exactly the same from the information you've posted.

Sounds like the DNO guy was just being a jobsworth.

You mentioned you took photos... I'm sure I'm not the only one who would like to see.
 
As there was an immediate risk to life through a potential fire risk I would have done the same thing.

If the DNO wanted to take it further, crack on and see you in court.
That's what I thought, I was just seeing what other people would have done in this situation as I have not come across this before. I thought the way the technician acted was really unprofessional as he was shouting at me in front of the client saying i didn't know what I was doing. Even if he wasn't happy with the way I did things he could have pulled me to the side and had a chat with me. Luckily in this case the client was a friend
We all can act out of turn, when faced with a stressful situation. I guess that's why the DNO engineer lost his cool slightly. I suspect, given the opportunity, he would have commended you for your actions, but would of calmly explained the dangers of what you did.

Seems you acted in good faith, and for the benefit of others. Having had time to reconsider, would you do the same again?
Yeah next time I wouldn't tell them I pulled the. Haha
I have withdrawn the DNO fuse in the past, the reason was the meter was smoking and arcing, I contacted the DNO for an emergency attendance and got he usual rhetoric on the phone about withdrawing the fuse and that it is illegal to interfere with their property, after telling them the reason their attitude quickly changed and it wasn't taken any further.

Having said this though, even in said situation there can be some big risks in doing so, especially if the cutout is damaged or aged, I have seen DNO cutout installers/upgraders on a few occasions refuse to touch the cutouts until power is removed upstream, when even the DNO won't pull the fuse live, you have to realise that the consequences can be deadly especially if you are ignorant to the possible risks.
I totally understood the risks and I felt it was the safest thing to do at the time, I would not have pulled them if there was any signs of physical damage or danger to the cut out itself
 
As several others have already said, and in my opinion, you did the right thing and I would have done exactly the same from the information you've posted.

Sounds like the DNO guy was just being a jobsworth.

You mentioned you took photos... I'm sure I'm not the only one who would like to see.
Like I say when I first arrived I didn't have my van on me so I had no way of telling What was live and dead, I presumed it had blown the main fuse but I couldn't be certain so I pulled the fuses. The whole lot was so hot you could barely touch it.


[ElectriciansForums.net] Pulling the dno fuse
 
@M1k3y1992

My post was a general approach or attitude to doing a DNO fuse withdrawal it was not in response to your situation directly , I think the Engineer was a prat for his approach and kicking off like that, like has been said, if there was an immediate danger to life or property IE it could burn the house down then if it is safe to do so you are allowed to withdraw the fuse and immediately inform the DNO of the situe', you did this and it seems you had the bad look to be attended by a self righteous 'jobsworth' (to repeat SparkyChicks words).. like you say it is lucky it's your friend or I would have been making a formal complaint to the DNO about their onsite attitude and manner.
 
Like I say when I first arrived I didn't have my van on me so I had no way of telling What was live and dead, I presumed it had blown the main fuse but I couldn't be certain so I pulled the fuses. The whole lot was so hot you could barely touch it.


View attachment 37903
Don't look like any DNO fuse to me.
 
done exactly the same a couple of times. both times DNO representative said i should not have touched it, but , off the record, he said it was the right thing to do. read that as you will.
 
Looking at the Photo I might have to partly agree that this didn't require you to interfere with the DNO's equipment, you had isolated the load and as long as you ensured no one went near the equipment or disturbed that cable(tail) then a DNO emergency call-out would have sufficed, given it in a metal enclosure with no real flammable parts contained in there I cannot myself consider this an immediate risk to life or property.. if concerned and as a qualified sparks you could have waited the usually 1 to 2hr response to ensure no-one got curious.

You would have had other options here too, you could with the correct PPE and insulated tools just cut the offending Tail at a safe point and dressed the live end with tape while you waited on the DNO, remaining on site meant this simple solution would have been fine although just taping the live end up and leaving would not be the right move, you would also need to inform the DNO engineer of your action so (s)he is fully aware of the small risk posed.

I suspect and with all the red tape we have to climb through nowadays with H&S that if you work for anyone then this may not have been an option but working live is a last resort and due to the situation I would say this could be done easily and safely with minimal risk with the correct equipment.
 
Myself, (and I work live a lot because of my line of work) I would have cut all tails and made safe, fitted henley blocks and terminated live and then replaced the switchgear and tailed up to the henleys.. but like I say, we live in times where you have to evacuate the shopping center because there's a crack in a light switch :O /

So for practical purposes of giving safe advice and limiting risk...Don't do this at home!
 
Looking at the Photo I might have to partly agree that this didn't require you to interfere with the DNO's equipment, you had isolated the load and as long as you ensured no one went near the equipment or disturbed that cable(tail) then a DNO emergency call-out would have sufficed, given it in a metal enclosure with no real flammable parts contained in there I cannot myself consider this an immediate risk to life or property.. if concerned and as a qualified sparks you could have waited the usually 1 to 2hr response to ensure no-one got curious.

You would have had other options here too, you could with the correct PPE and insulated tools just cut the offending Tail at a safe point and dressed the live end with tape while you waited on the DNO, remaining on site meant this simple solution would have been fine although just taping the live end up and leaving would not be the right move, you would also need to inform the DNO engineer of your action so (s)he is fully aware of the small risk posed.

I suspect and with all the red tape we have to climb through nowadays with H&S that if you work for anyone then this may not have been an option but working live is a last resort and due to the situation I would say this could be done easily and safely with minimal risk with the correct equipment.
Thank you for your response, the dilemma i had was the client needed to be up and running as soon as possible. Yes i could have taped it up and waited, and in a circumstance where time was not an issue I would have considered this, but as you can imagine I was under pressure to get power back on asap. With regards to henly blocking the tails, I did this job on a Saturday when wholesalers are all shut and I don't have the parts on my van, but I probably wouldn't have done that live. I did what I thought was best in the moment to immediately remove the hazard.
 
Last edited:

Reply to Pulling the dno fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
649
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
816

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top