SparkyChick
Broke Internet
Supporter
Hi all,
As the title suggests, I'm looking for a little bit of guidance.
Long story short... kitchen remodel, was asked to install a heavy duty supply for an induction hob on short timescales as ceiling was going to be closed.
Only sizeable cable I had to hand was 10mm.
Now, in a happy turn of events, it turns out that the induction hob isn't that hungry and only needs to plug in, but the oven and microwave also require supplies. None of them are over 16A.
So my original plan was to install a BG shower CU, switch out the breakers for 16A (one for each appliance) and supply this using the 10mm on a 50A breaker from the main DB. The new CU was to be mounted on the wall, making an obvious accessory safety zone.
However, due to the construction of the kitchen units, I felt it better to have the CU inside a cupboard rather than cut a portion of the backboard away.
Where I'm seeking guidance is that this now means the 10mm is concealed in the wall, from ceiling to just below the top of the cupboard. Along the rest of it's run, it is installed in a manner (i.e. it's not at risk of damage and it's not concealed in a wall) that means it's fine to be connected to the non-RCD side of the board (the new CU has RCD protection in it).
So I have a length of cable about 10-12" buried in the wall. Due to it's location I don't believe it is at risk of being damaged by screws as it is unlikely anyone will want to hang anything there because it's effectively behind the cupboard.
I have placed a warning sticker on the top of the cupboard (Danger Concealed Cable - This includes an arrow aligned with the vertical drop of the cable). I'm going to record full details on the certificate of the location of the cable and my reasoning as to why this is acceptable.
Acceptable or not? Is this kind of departure allowed in domestic and if so is it sufficient to include your reasoning in the certificate or is there a template risk assessment I would need to use?
Your comments and thoughts are most welcome :)
So, an update...
The issue of capping... none of my local wholesalers had anything resembling the capping LSK has suggested and I would go so far as to say they didn't understand why standard capping wasn't good enough until I explained it was a requirement for avoiding RCD protection on cables buried less than 50mm from the surface. If I want it I'm going to have to purchase directly or find someone who can ship it.
I ran the numbers on the board and initially concluded that the main switch (100A) and the RCD (100A) (which upon closer inspection had spare ways) would be pushed over the edge, so I picked up another board, henley block, new tails etc. But I also picked up my OSG and then re-ran the numbers and my initial view was a little off.
The existing board and the RCD had sufficient headroom to allow me to utilise a spare way so the cable is protected by an RCD at the origin, so everyone's happy :)
I was a bit concerned about the overall load on the CU but I think on reflection I was more concerned than I should have been as what's actually happened is a 32A cooker circuit has been replaced by two cooking appliances (rated 15A and 16A), the stand alone microwave is going (one of the new appliances is a fitted microwave) so all that's been added is the hob.
And to boot, it appears based on the test in GN8, with a resistance to the MET of 52k ohm, the water doesn't need it's bonding reconnecting which begs the question... why was it bonded in the first place?
So all in all, not too bad a day despite my concerns about this.
Thanks for all your input chaps.
I remember a time when you were in danger of getting the cutlery bonded if you weren't careful. A very contentious and misunderstood area for a lot of electricians. I use that word advisedly!
SparkyChick
Broke Internet
Supporter
South Wales
Website
http://www.sparkychick.uk
Business Name
SparkyChick
Domestic Departure from BS7671 - Advice
Domestic Electrician Forum
SparkyChick,
Toneyz,