Thinking about the hole I would not code 2 for fire reasons because as long as all the terminals are tight its not going to catch on fire , but might code 2 it due to the amount of dust debris that could build up inside the CU and get into the terminals due to the large hole.
Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
You have bs 7671 as reference.
It can be considered a C2 if it’s a fire barrier as per section 527
Napit are wrong then.
I disagree. If someone was to plug something in
527.2.1 is the reg attached to the coding in the napit book. Obviously there will be no mention of coding in the regs but again i would rather have a reference, although i agree not gospel.
There is no right or wrong answer its down to the persifics of each situation and you make a judgment call on it I will stick with my code 3 but would not judge someone else if they where to code 2 it .
The idea is tho that you are now outside the equipotential bonding using outdoor equipment so I’d agree that if socket outlets that are not likely to be used outdoors and this is carefull considered by the inspector perhaps in conjunction with the client, then I agree a C3 at worst for no rcd protection to sockets.
You are coding against additional protection to the user and not the equipment plugged into it
For a specific socket used as in the op for a fridge it can’t possibly be a C2 code
The sockets are not labelled, no risk assessment and they are not being used for the fridges in alot of the rooms. The client also said that he often finds the fridges have been unplugged as there isnt enough sockets in the rooms
If the swa is glanded at the supply end and the armour is at least connected to earth, I can’t see how it can possibly be a C2 unless there is signs of mechanical stresses on the cable at the load end?
Cant see above the DB to see if its cleated well and they all seam to be coming in at angles. Its all together rough so ill stick with C2. If i was to share some of the communal areas you would agree. The rooms are good compared.
I think youd agree that it is rough and would prefer to see the DB installed properly and stick an rcd socket on the socket not protected as again the client has stated people unplug the fridge and use it for all sorts.
Does it give a reason for this? , also is a hotel classed as commercial I thought they would be classed as simply a hotel
Yes its classed as commercial premesis.
Regarding the socket, it's a code 3 for me, however in these circumstances I always add an advisory note that the provision of RCD protection is strongly recommended. Given that under a very recent edition of Bs7671 the provision of a socket outlet for a specific item of equipment was permitted without RCD protection it is very hard to justify a 'potentially dangerous' code.
But the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
We do not know the conditions under which this instal was done,
It seems to be mostly what people might call sloopy work,
Or not " Best practice " but it is not really dangerous,
it's just not best practice.
Many electrical instals are done to a lower standard,
yet last for decades with no problems.
everything can always be done better
It’s the 18th now.
All socket-outlets must have RCD protection.
Risk Assessments are out the window.
Risk assessments are not out of the window on non domestic installations 411.3.3 an exception to (i) is permitted where other than an installation in a dwelling, a documented risk assessment determines that rcd protection is not necessary
conrad,