Hi. We are looking to quote to install domestic heat detectors interconnected to the existing smoke alarms for a social housing provider. Do you think that FP200 could be used to save us installing RCD protection to the circuit as the cable needs to be concealed. Our NIC inspector tells me that t and e can't be used through the ceiling void because you can't guarantee that it's at a depth of 50mm, so FP would seem to be the way forward. I am aware the the cable is fully screened but only by a foil wrap. Cheers.
 
why can't you clip the T&E at a height of more than 50mm if it is in a ceiling void?
 
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.
 
Last edited by a moderator:
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.

But the 'earthed metalic sheath' that they are referring to in the regs, (in order to not need RCD protection), is for mechanical protection.

FP200 sheath does not offer this.

SWA, yes. Steel conduit, yes. Earthed steel plate, yes. But not FP200.:)
 
Last edited by a moderator:
I would have thought that the purpose of earthed metallic sheath was to provide automatic dis connection rather than mechanical protection.
 
It's not a matter of mechanical protection, more earthed metallic sheath. Without lifting floorboard, carpets and moving furniture, cable can not be clipped. We are talking about 5000 properties, if it was just a few would not be an issue.

and how would you earth the foil? sy would be better.
 
I would have thought that the purpose of earthed metallic sheath was to provide automatic dis connection rather than mechanical protection.

You might actually be right with regards to the requirements of that regulation - I've always took it as 'earthed mechanical protection' that was required - I've never thought of it from the point that you're making, but I've just re-read it.:)

So the question, as you were asking, is 'does FP200 fit the bill?
 
Last edited by a moderator:
How exactly would you "terminate" foil???

Standard FP 200 should be treated the same as T&E.
 
I had a similar issue with interconnecting alarms and concluded with the use of radio linked alarms. I was initially concerned about compliance, however the manufacturers verified it's compliance with Part B 1.21.

The only issue was location, however positions were acceptable in close proximity to lighting points, and the rigidity of the fp200 enabled a 50mm clearance from point to point.

Mr NIC man and Mr Building Inspector were both happy.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Can FP 200 be burried in the wall without RCD???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
wetny,
Last reply from
Sparky Ninja,
Replies
15
Views
12,960

Advert

Back
Top