No as in there isn't a regs breach? What about the regs that states MCB's must be of the same make, would it fall under the general rule of that one.No, as you say. I would agree.
Is that a definite as I have to get back to them ASAPQuite simply, the 'council BOD' is an idiot.
The thing is I know that its perfectly safe but I'm up against a public sector drone who's sole purpose in life will be to make other people's life a misery so if there is even the slightest chance that there is anything technically wrong with it then it will get flagged.There is no such thing as a 'regs breach'. BS7671 is not a statutory document, but a collection of guidelines to be interpreted by a competent person. Since the dimensions of a DIN rail and the size and position of the slot in the panel in front of it are standardised, there is no problem there. A SPD does not produce heat in normal times - it just sits there, so no problem there.
As long as you are competent enough to judge if the distance between the terminals on the SPD and the back of the front panel is adequate, and that the SPD projects far enough though the panel so that there are no IP problems, then it's fine.
The only reg I can find is 536.4.203 which states that
"in consumer units incorporated devices and components shall only be those declared suitable according to the assembly manufacturers instructions."
There are quite a few people who wouldn't be happy to have a BG anythingYou should ask Crabtree if they're happy having the BG SPD in their board. They're usually pretty good at answering emails quickly, and you have the answer straight from the horse's mouth.
I asked this question of an SPD manufacturer (Surge Devices) at a trade fair. They said exactly what you said.If an SPD is installed from an MCB and not directly on the busbar system, it does not affect the integrity of the consumer unit.
Also, as an SPD is a voltage detection device, it does not have a short circuit withstand capacity, such as an MCB, so does not require type testing to any specific manufacturer.
I take umbrage.I asked this question of an SPD manufacturer (Surge Devices) at a trade fair. They said exactly what you said.
Random thought, but did you spend a day in Manchester wearing a dress about a year ago?
Hmm I've heard this is quite common in your area of Cornwall.I take umbrage.
It was more than a day and I also wore more than one dress.