Hi guys. I’ve just done an eicr on a flat and they need a fuse board upgrade. Now the tails are still 16mm and there protected by a 60a fuse. And the main cut out is 80a. Do I have to change the tails? The board is at least 10+ meters away, concrete ceilings, have to wire through boxing in, all round the bathroom before I get to the board , so armoured cable could be very very difficult. They don’t plan to upgrade anything high powered like ev charger etc. at the moment they have really just lights / sockets. They have a power shower cable in (just in case they change over) and they also have oven cable in and might be changing to electric oven (under 2kw) electric hob. So the tails can take the power. I was just wondering if it’s mandatory to upgrade or if I can just note it down on eicr / eic when I change board that they didn’t get changed. Thanks guys