Hi guys. I’ve just done an eicr on a flat and they need a fuse board upgrade. Now the tails are still 16mm and there protected by a 60a fuse. And the main cut out is 80a. Do I have to change the tails? The board is at least 10+ meters away, concrete ceilings, have to wire through boxing in, all round the bathroom before I get to the board , so armoured cable could be very very difficult. They don’t plan to upgrade anything high powered like ev charger etc. at the moment they have really just lights / sockets. They have a power shower cable in (just in case they change over) and they also have oven cable in and might be changing to electric oven (under 2kw) electric hob. So the tails can take the power. I was just wondering if it’s mandatory to upgrade or if I can just note it down on eicr / eic when I change board that they didn’t get changed. Thanks guys
 
Hi guys. I’ve just done an eicr on a flat and they need a fuse board upgrade. Now the tails are still 16mm and there protected by a 60a fuse. And the main cut out is 80a. Do I have to change the tails? The board is at least 10+ meters away, concrete ceilings, have to wire through boxing in, all round the bathroom before I get to the board , so armoured cable could be very very difficult. They don’t plan to upgrade anything high powered like ev charger etc. at the moment they have really just lights / sockets. They have a power shower cable in (just in case they change over) and they also have oven cable in and might be changing to electric oven (under 2kw) electric hob. So the tails can take the power. I was just wondering if it’s mandatory to upgrade or if I can just note it down on eicr / eic when I change board that they didn’t get changed. Thanks guys

What is the cable used at the moment?
 
16mm tails are good to 80A providing everything else checks such as VD and Zs no need to update.
Zs was 0.15 on a Tn c s. I believe they are clipped direct but I can’t confirm that. Ceiling is concrete , I doubt they would have put it in the ceiling.

Thank you for the reply brother!
 
Zs was 0.15 on a Tn c s. I believe they are clipped direct but I can’t confirm that. Ceiling is concrete , I doubt they would have put it in the ceiling.

Thank you for the reply brother!

Sorry was a bit quick on the draw regarding 16mm tails they are good to 80A normally but this is 10m you say clipped direct is that double insulated singles?
 
Sorry was a bit quick on the draw regarding 16mm tails they are good to 80A normally but this is 10m you say clipped direct is that double insulated singles?
Double insulated singles yes. And I think clipped direct. It’s in a flat. With a flat above so it’s concrete ceilings. I would like to think it’s clipped direct but I can’t confirm.
 
Also anyway of checking volt drop without calcs? As I don’t know true length?
If you don't know it then it would be fine to estimate it you shouldn't be that far out. I doubt VD will be a problem but always worth checking as that would be another reason to upgrade the tails.

16mm tails in free air is good for 80A but in this case you need to do the calcs with regard to the reference method. Probably 16mm won't cut it when you do the calcs.

I guess you can ask the client if they want it upgraded now or when they might need it?
 
If you don't know it then it would be fine to estimate it you shouldn't be that far out. I doubt VD will be a problem but always worth checking as that would be another reason to upgrade the tails.

16mm tails in free air is good for 80A but in this case you need to do the calcs with regard to the reference method. Probably 16mm won't cut it when you do the calcs.

I guess you can ask the client if they want it upgraded now or when they might need it?
Nice one thank you brother. I’m in two minds about it. If I was to upgrade the tails. I would like to install flexi tails. But that means running them all through boxing in with pipes etc / and 10+ meters. Now I know I can put a fuse isolator with th meter. Just don’t know if it’s a bit bogey/ and or it should probably really be a armoured. But I’m definitely not getting the armoured in the boxing in. I’ll ask the client see what they think. I believe he’s going to rent it out to uni students (1 bed flat) so it shoukdnt really pull a lot of power
 
Double insulated singles yes. And I think clipped direct. It’s in a flat. With a flat above so it’s concrete ceilings. I would like to think it’s clipped direct but I can’t confirm.
That is tricky, 10m is a long run and they could be subject to one of the derating factors along its route which you cannot confirm.

Clipped direct is good to 87A even enclosed in thermally insulated wall is 61A So all good on a 60A Fuse

If they ever want to upgrade to 80A then the cable run would need to be verified that it is fully clipped direct.
 
That is tricky, 10m is a long run and they could be subject to one of the derating factors along its route which you cannot confirm.

Clipped direct is good to 87A even enclosed in thermally insulated wall is 61A So all good on a 60A Fuse

If they ever want to upgrade to 80A then the cable run would need to be verified that it is fully clipped direct.
Yeah! T going to talk to client tomorrow! Thanks a lot brother!
 
Nice one thank you brother. I’m in two minds about it. If I was to upgrade the tails. I would like to install flexi tails. But that means running them all through boxing in with pipes etc / and 10+ meters. Now I know I can put a fuse isolator with th meter. Just don’t know if it’s a bit bogey/ and or it should probably really be a armoured. But I’m definitely not getting the armoured in the boxing in. I’ll ask the client see what they think. I believe he’s going to rent it out to uni students (1 bed flat) so it shoukdnt really pull a lot of power
Is any part of the tails concealed within a wall or partition.
 