P
philn
Hi there. Im new to PAT testing. I am confused as all the fridges/freezers I have looked at range from 55 watts to 135 watts and from what Ive been taught any appliance under 700 watts requires either a 3 or 5 amp fuse. However, all the above that I have seen have a 13 amp fuse and the CE rating plate says 13 amp. So what am I to do? Do I go by the rating plate or follow what Ive been taught and change the fuse? Answers greatly appreciated thanks :-)
basically, the fuse in the plug is to protect the flex to the appliance in the case of overload or short circuit. as the flex on fridge /freezers is generally 1.5mm, 13A is correct. bear in mind that the appliance is basically a motor, which starts and stops frequently thru the stat, and so you will get repeated surge currents which will cause fuse blowing if 3A or 5A.
Ok thanks for the reply teletrix. So the below 700 watt rule isnt hard and fast then? If the appliance says it needs 13 amp then you go by that?
yep. manufacturers stipulate the fuse rating. the 700 watt rule is more for appliances not having motors or other devices which have a high surge current.
hi my fridge is a sumsung and it keeps blowing a 250ma fuse on the top of the fridge
The above thread discusses the fuse rating in the mains plug supplying the fridge.
I expect that the 250mA fuse is protecting an internal fridge circuit.
you need to have an appliance engineer investigate it, maybe one that specialises in Samsung.
also worthwhile checking with samsung if there's a recall on your model. could be an intrinsic fault.
I've been doing appliance testing for tears never seen a fringe freezer underer 13a
I think the 250mA fuse referred to earlier is probably an internal one within the fridge itself. Maybe protecting a control module or something.
oh how I wish that I had thought of that
Ah looks like I did! #smugbarsteward
philn,
DPG,