Pip
Hi People,
Looked at a job today which requires adjustments to the CU and noticed there is 16mm from CU to MET which is cool, 10mm from MET to Gas main incoming, and bonding between all pipes coming in and out of the boiler linked off the GAS main bonding.
When I pointed out that there should be a 10mm to the mains water incoming the customer informed me that there was not one fitted as the incoming pipe is plastic, and most of the fittings in the house were a mixture of plastic and copper, so would be no use as an earth bond.
I could see his point, but where do we stand on such a situation?
Pip
just had a quick look at that pdf. it's 16th, out of date.
that was brought up last time we used it, but until something more resent is brought up..?...?...?
The reg I quoted is to date, and informs us that PVC supplied services with metallic framework downstream can be subject to bonding.
I thank you very much, it has been very enlightening, after I put up the post, I did look closer on the site and yes I can see why you are getting your De Ja vu, the question has been asked a few times recently, with some conflicting answers, which what you expect on such a subject
Again many thanks Pip
A plastic incoming service cannot, by definition, be an extraneous conductive part, ie. a part that is liable to introduce an earth potential or any other potential into an installation. Therefore main equipotential bonding is not required.
There is a standard test, described in GN8, to confirm whether an incoming service is or is not an extraneous conductive part. Using a high-reading ohm-meter, resistance is measured between the part and the MET of the installation. If above 56K Ohm it is not an extraneous conductive part.
but still not resolved in my opinion, sitemanager insists its not fitted, qs insists that a bond is made to wherever the incoming plastic turns to copper (wherever that may be), niceic are supposedly going to get back on this one, as stated earlier i would always bond at the first available place but it would be nice to get a definitive answer on this one.
When you say wherever the plastic changes to copper, are you talking about say 1 metre of copper, 8 metres of plastic, another metre of copper etc?
no mate copper incoming direct to stop tab then plastic in bathroom, goes underground and reappears near to combi which is the next closest place to put the bond.
one next door has copper intake then about 2 metres plastic returning to copper in same room, so a clamp can go on to the coper near the stop tap.
interested in your views on this as i still think a bond should be put in wherever the first point is that you can fit one. Everyone seems to have a diffent opinion.
Hi where do you get that value from? The figure of 22KΩ sticks in my mind but tbh i can't remember off hand where i saw that.
When I spoke to one of the niceic's long standing engineer inspectors, he said you don't bond plastic water incomers, but if you want to do it, then don't bother asking me in the first instance.
He was the same person who said he does not agree with own technical team of technician's who say the existing bonding clamps attached to a lead incomer are unsuitable.
Therefore imo the niciec inspectors appear to interpret BS7671 differently from their own technical team, but they always say your the one signing the sheet. So I would do what I was happy with, no matter what I'm told by others.
And will never be told how to carry out my job by a QS or Site Agent and many other non Electrical trade person. You have a Duty of Care, that's where it Stops.
thata a good point so my view stands a main bond will be fitted at first available point (wherever that may be)
Fit the bond, your the electrician and you have a duty of care, and your name will go on the sheet in the one and only box of: designer, installer and tester.
I never do what I'm told to do if I'm not comfortable with it, end of.
Ive just gone on a job, ripping out 25mm bonding cables and running in new 50mm ones, I'm not sure there needed, but I'm not signing any sheets.
Must admit I have never seen non-copper bonding cables at 25mm^ is that a new install and they got it wrong.
These are copper.
Non PME systems need not exceed 25mm, but this is a PME system and the run is a good 35/40 meters and I think they maybe referring on Table 54.8, but I'm not sure if the main supply cables exceed 150mm.
Now if the continuity ohms reading was exceeding 0.05, then that maybe a factor.
I'm already get ----ed off being told what to do, Ive already put so called technical people in a corner with a bit of BS7671 theory and its surprising how many older people out there are blagging their way through lol
Ok if this topic is going to go on and on, can we discuss what's wrong with the reg?
These are copper.
Ahh right there PME I though you may have had a engineer not exactly reading the BRB right.
The answer to the question is soooooo ssssssimple. if it's copper bond it in the usual way. if it's plastic, I can supply an endless quantity of plastic zip ties, quick to fit and just clamp the insulation of the bonding conductor under the tie. better still, as it's plastic pipe, just use a bit of green/yellow sleeving as the bond. makes everything look kosher for the jobsworth building inspector.
as widdler states 544.1.2 as near as practicable or after any insulating section. which is the only reg that actually gives any real wording on the matter. but with a site manager, qs and unresponsive advice from niceic i think the area should be addressed a bit more clearly within the regs.
eitherway im fitting bonding at first available point wether it returns to plastic, copper or kryptonite and they can all go jump!
welll said. totally agree with you
Now thats what I call free thinking and good on you for that attitude
All of us who may "think" we understand the objective of the regulation, has right on our side
If that objective is made much more definitive by the regulation makers,everybidy, the pretend regulation makers, (we know who that is) and sparks everywhere should be "as one" with the interpretation of what and where to bond
It does need sorting
If you feel there's a reasonable possibility that the pipe in question could introduce a potential, then you have make that final decision, to bond or not to bond :)
Ive seen plenty of sparks run a 10mm into the cylinder cupboard, and cross every pipe to make sure.
I use 23K Ohm, derived from a 10mA fault current.
This is the overall value i'm thinking of but when you measure it you are looking for 22kΩ as you take the human body to have a resistance of 1000Ω.
Lenny (re that link) i would not be happy with taking 6667Ω as the value for an extraneous conductor as that could allow 29mA of current to flow and a grip response (ie the person being shocked can't let go) can be exhibited at 20mA. whereas the 23kΩ figure gives 10mA to which the body response is release/jump back. Surprised that niceic put their faith in that value.
DETERMINING IF A PART IS EXTRANEOUS OR JUST A PIECE OF METAL
A test should be made using an Insulation Resistance Tester set on MΩ, supplying 500 Volts.
Test procedure:
Connect one test lead to the metal part and the other lead to a known earth. (MET)
If the resistance value is 0.02MΩ (20000Ω) or greater, no supplementary bonding conductor is required.
If it is less than 0.02MΩ, supplementary bonding should be carried out.
From the Ohm’s law:
I = V / R; I = 500V / 20000Ω = 0.025Amp
This shows that if the fault was on a single phase 230Volt supply the current that would flow between the conductive parts would of course be only 0.012Amp.
This current is unlikely to give a fatal shock
GN8 and GN5: if extraneous metalwork is above 22KΩ then it need not be supplementary bonded.
only problem as i see it is, what IR testers or MFTs have that kind of accuracy at such a low value?
16th Edition citb study notes used to state 0.25 megohm, but with a visual inspection. So I suppose if you can not inspect the entire length of the metallic object, you should not rely upon the test alone?
Pip
Ebrington, GL55
Website
https://www.pipelectricalservices.co.uk/
Business Name
P.I.P Electrical Services
How can you Earth Bond plastic incoming mains water pipe?
Pip,
tonys,