Is it true that NICEIC requires that the PIR testing is the 100% of the installation? I have always tested around 50-60%, but now I have client who is saying that the NICEIC wants 100%.

Anybody knows about this?

thanks!
 
In order to be really valid a PIR has to be 100%....the recommendation is that if sampling a percentage of the install shows up problems then 100% will be necessary.After all an partial PIR on a suspect install will leave a host of unfound issues....common sense really.
 
Visual inspection, or sampling of, can be agreed at a percentage depending on initial findings i.e, you state 25% of accessories inspected. If this shows up any hidden nasties then it should be increased to 100%.

As for physical testing of final circuits I always perform 100%, unless there are any agreed limitations due to access & inconvenience etc.
 
You could also argue that 100% would mean chasing the wall out!

True. To just state 100% visual inspection would indicate that this is the case which is where the word 'accessories' comes in.

I also note items like in my limitations - cables buried within building fabric & beneath floors are not visually inspected.

Setting out exactly whats what is key IMO.
 
Its the client who decides,not the niceic,whatever they do or do not want inspected and tested is up to them as they are the ones paying for it,i was called today from a howmeowner who says she had a new consumer unit fitted 4 years ago,the sparky who did the job did not issue any test certs,they think he is retired as can not contact him,she wanted a cert because without it the sale is off,so the only thing to do is a periodic.
 
Sdandard limitations are listed in the BRB BGB so there is NO way you can perform 100%test without ripping walls ceilings ect to bits Tell the client to stop being a bellend n accept your findings
 
Hi guys,

Is it true that NICEIC requires that the PIR testing is the 100% of the installation? I have always tested around 50-60%, but now I have client who is saying that the NICEIC wants 100%.

Anybody knows about this?

thanks!
When it comes to testing for IR, you test all the final circuits, for finding R1+R2, you check all the light sockets & sockets on radials and you will read Zs on all the sockets on the ring (live test) – so how do you test 50-60% of the installation? Do you pick ‘n’ choose the circuits and sockets at random?

...and if all the sockets are not tested, what would one put down on the test sheet?

Cheers!
 
NICEIC's book BS 7671:2008 17th edition Learning Guide states

"The periodic inspection and testing procedure does not require all equipment to be inspected or all tests to be carried out. The emphasis should be to assess which areas require inspection or tests on a risk basis. Because some dismantling may create problems the regulations recommend either no dismantling or partial dismantling, supplemented by appropriate tests. It is important that precautions are taken to ensure that the inspection and testing does not cause danger to persons or livestock or damage top property and equipment even if the circuit is defective."

This is from there own litrature, so unless they changed their tune I would say they endorse sampling. Though I agree with above posts, if any faults are found then 100% should be done.
 
Hi guys,

Is it true that NICEIC requires that the PIR testing is the 100% of the installation?

Which part do you mean? Removal of accessories etc? I agree with the others here that you should be testing 100% of the readings but not removing all switches etc. If it the accessories that you mean, NIC did a video a year or two ago where Tony Cable or whatever he's called said that you dont need to remove everything. i have never resorted to taking everything off - you just dont need to unless you find something that warrants further investigation
 
Lets be reasonable here. A PIR cost around £120 to £150. If you would do a full 100% of the installation then you might as well go being a laborer for the money you earn.

Also, it is simple common sense to not remove every single light fitting, is it not?

I always fully test the ring, the shower and the cooker circuit. The rest I sample. If that is not good enough I will stop doing PIR`s because simply I can earn more pulling in cables and not worry about anything at all.
 
In what way do you sample the circuits? (not having a go - just curious) That NICEIC video i mentioned states you can do a global test on your board with all fuses / mcbs in. I am old school and prefer to do them one by one, although it does take a lot longer. What reading s do you put for the cicruits you havent tested?
 
In what way do you sample the circuits? (not having a go - just curious) That NICEIC video i mentioned states you can do a global test on your board with all fuses / mcbs in. I am old school and prefer to do them one by one, although it does take a lot longer. What reading s do you put for the cicruits you havent tested?
LIM, I guess or just make it up, LOL
 