I really don't know where this has come from, certainly not from NICEIC.
The reason for DETAILED INSPECTING of a percentage of accessories/luminaires/switchgear etc. is that faults will actually be created as a result of opening enclosures, disconnecting and reconnecting cables etc.
This is why the inspector should have an above average knowledge of BS7671 and very good experience of the type of installation being inspected, in order to make good engineering decisions.
Competency is a good mixture of education, experience and knowledge, sadly lacking in the majority of PIR's that I see regularly!
The requirement for diagrams/charts etc (assuming their absence) will normally be highlighted as a defect on the report unless the original scope of work was to complete these as part of the inspection.