Had a phone call to go and look at moving a 44kva 3 phase generator on a farm. Im going to have to resupply it in swa. I havent done any work on a farm and i ve only ever installed temporary generators when the electricity board have decided not to turn up a day before a shop opens. I am thinking i should bury the cable 0.6m as per regs. Does anyone know if it has to be bureied. The guy on the phone was talking about taking it over a building but i want it to be done to regs. Any other advice would be greatly appreciated

Thanks guys
 
There is no reason it has to be buried other than if you do it should be deep enough that it will not be damaged hence the recomended depth of 600mm or if it is going surface it should be placed where vehicle or livestock damage will not happen, However from past experience on farms I would think carefully on the route underground as layouts change contantly with fenceposts etc.
Best advice is to keep to straight lines with solid markers (buildings etc) at direction changes, go deeper if you can and give them a layout drawing to stop damage to it later not forgetting marker tape above its route.
My guess its for a standby with auto or manual changover so earthing should also be checked but i'm sure you have that covered.
 
when you eary your genny, try to get a low reading as possible.This will entail driving 2 or more seperate rods down, at least the same distance as the deepest rod apart. Also any metalwork that can be touched at the same time as the genny frame, will need to be bonded to the genny.
 
Last edited by a moderator:
when you eary your genny, try to get a low reading as possible.This will entail driving 2 or more seperate rods down, at least the same distance as the deepest rod apart. Also any metalwork that can be touched at the same time as the genny frame, will need to be bonded to the genny.

Far better to have one rod position and coupling the rods to give you the depth, rather than having 2 X 1 metre rods in 2 positions. Even better, to have the 2 rod positions each with 2 rods coupled together!!

What is important is to make absolutely sure your neutral point on the Genny is earthed via your rods, and not just bonded to the Genny frame.
 