the genny should be bionded to any metalwork that is within reach.
The normal convention is to run a 4core cable (3ph) and an earth, or 5 single cores.
gennys may only be used together if it is possible to syncronise them together, to prevent strange voltages. If this is not possible then no, it will not be allowed.
the supply will only need RCD protection if the Ze/Zs values mean that the protective devices will not
operate within specified times.
The normal convention is to run a 4core cable (3ph) and an earth, or 5 single cores.
gennys may only be used together if it is possible to syncronise them together, to prevent strange voltages. If this is not possible then no, it will not be allowed.
the supply will only need RCD protection if the Ze/Zs values mean that the protective devices will not
operate within specified times.