Discuss 3 phase generator help in the Commercial Electrical Advice area at ElectriciansForums.net
Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator has 3 motors 11hp, 5.5 hp and 3hp. The 11hp motor kept tripping the gennys mcb so a previous spark fitted an adaptable box with contactors so it now starts up on star delta.
The genny is on a trailer and the 11hp motor pumps the Slurry upto the separator at the front of the trailer. The 11hp motor will be about 10-15m away from the trailer so he has asked me to make up an extension lead using swa and commando sockets as there could be livestock close by. The 11hp motor is protected by a 20amp ctype mcb, the 3hp motor has a 10amp mcb, the 5.5 hp motor is new. I couldn't see an Rcd anywhere on the genny.
The farmer went and bought 6mm 5 core swa and commando sockets before I got there.
As the 11hp motor is pulling about 11amps a 2.5 would be enough, it will have to be 7 core for the star delta, iv found 7 pin commando plug/sockets online.
He does want it hard wired because of the high risk of the cable getting damaged.
Would it be OK to solder a 2.5 earth onto the swa heat shrink it, and connect it to the commando male/female, then protect it with a 3phase RCD. Or go for a HO7 cable for extension lead..
Also anyone with advice for earthing for a portable genny would be helpful, it be attached to any other installation just the 3 3phase motors..
Thanks in advance
SWA is unsuitable for making up trailing leads, it is not suitable for regular movement and flexing, you need flexible cable for this.
HO7-RNF flex is a heavy duty flex which may be appropriate.
I'm not sure you'll find a suitable commando plug/socket to do this, I don't think you can get a 7pin 400V/50Hz one.
The only 7 pin commando sockets I've seen have been the purple ones, which I think are for ELV.
If the cable is likely to get damaged then find a different route for it where it is not going to get damaged or provide protection for it.
Thanks for the reply, iv sourced 32a ip67 6p+e sockets/plugs. Iv went with the swa it will be permanently fixed at the supply side and a commando socket at the load side, il have to solder the earth onto the swa.. its not ideal but the fact there could be live stock and with the way the plant has to be packed away swa should give it the best chance of not getting damaged.. it will be protected with a 30ma rcd..
Reply to 3 phase generator help in the Commercial Electrical Advice area at ElectriciansForums.net
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Hello everyone, I really hope this isn't an idiot question but boy, I'm out of my depth! I've spent about 3 weeks (not solid mind) trying to work...
Hi Everyone May be someone could shed some insight on the sizing and provide some suggestions: 3 phase Generators (400 V, 50 Hz) have the...