Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator has 3 motors 11hp, 5.5 hp and 3hp. The 11hp motor kept tripping the gennys mcb so a previous spark fitted an adaptable box with contactors so it now starts up on star delta.
The genny is on a trailer and the 11hp motor pumps the Slurry upto the separator at the front of the trailer. The 11hp motor will be about 10-15m away from the trailer so he has asked me to make up an extension lead using swa and commando sockets as there could be livestock close by. The 11hp motor is protected by a 20amp ctype mcb, the 3hp motor has a 10amp mcb, the 5.5 hp motor is new. I couldn't see an Rcd anywhere on the genny.
The farmer went and bought 6mm 5 core swa and commando sockets before I got there.
As the 11hp motor is pulling about 11amps a 2.5 would be enough, it will have to be 7 core for the star delta, iv found 7 pin commando plug/sockets online.
He does want it hard wired because of the high risk of the cable getting damaged.
Would it be OK to solder a 2.5 earth onto the swa heat shrink it, and connect it to the commando male/female, then protect it with a 3phase RCD. Or go for a HO7 cable for extension lead..
Also anyone with advice for earthing for a portable genny would be helpful, it be attached to any other installation just the 3 3phase motors..
Thanks in advance
The genny is on a trailer and the 11hp motor pumps the Slurry upto the separator at the front of the trailer. The 11hp motor will be about 10-15m away from the trailer so he has asked me to make up an extension lead using swa and commando sockets as there could be livestock close by. The 11hp motor is protected by a 20amp ctype mcb, the 3hp motor has a 10amp mcb, the 5.5 hp motor is new. I couldn't see an Rcd anywhere on the genny.
The farmer went and bought 6mm 5 core swa and commando sockets before I got there.
As the 11hp motor is pulling about 11amps a 2.5 would be enough, it will have to be 7 core for the star delta, iv found 7 pin commando plug/sockets online.
He does want it hard wired because of the high risk of the cable getting damaged.
Would it be OK to solder a 2.5 earth onto the swa heat shrink it, and connect it to the commando male/female, then protect it with a 3phase RCD. Or go for a HO7 cable for extension lead..
Also anyone with advice for earthing for a portable genny would be helpful, it be attached to any other installation just the 3 3phase motors..
Thanks in advance