Just fitted dual RCD consumer unit. Wiring old and no earth on light circuits. Customer does not want me to disturb newly decorated and new carpeted house so new consumer unit with testing is as far as i can go.
However, on fitting consumer unit, at least four circuits trip the RCD. I tested insulation values before i started the change and all were ok. Even though wiring old it still looks in good condition.
With the suspect circuits off RCD stays on but test button in effective. Circuits on and it trips.
If I put all circuits on same RCD it still trips.
Any ideas on best way to find the problem. Currently left without RCDs connected ( not good but at least MCB board better than old rewireable board removed)
Sounds like you may have interconnected neutrals somewhere in the house. If it's old as you say there are going to be jb's under the floors, in the loft etc and you never know whats been connected to what. I would start by checking for continuity between the lives and neutrals to see whether that is the case. Could be a right mare!
I bet that's cheered him up no end!!! ...lol!!
Yuk! not a nice position to be in. What are the 4 circuits? How are the IR readings when the circuits are tested individually?
What tests did you carry out for the purpose of your EIC?
Also, with no cpc on the lighting circuits, are all the fittings class 2?
What make was the new board? I've had Contactum boards on more than one occasion where the neutral cables from the main switch to the RCD's, and RCD's to neutral bars are not routed correctly. It caused the RCD's to trip as soon as any circuit was energised.
good call...... @ OP. check all manufacturer's connections and make sure you've got all your neutrals in the correct neutral bars.
sounds like a borrowed neutral or 2. as already said check your neutrals are in the right place in cu. have you tested rcd's? could be faulty.
OP, you wouldn't be the first to mix up Neutrals. I managed to do it myself and there were only four circuits only two of which were on the RCD side lol
Have you separated the upstairs and downstairs lighting circuits? If so, is there a 3 core cable going from the hall switch to the landing switch? Often on older properties there is no 3 core only a single running from one switch to the other.
There are many reasons why this could happen. Best thing to do is take a deep breath and don't panic, clear your mind and think as more often than not the problem is often staring you in the face.
Good Luck, I look forward to hearing how you get on :thumbsup
I've had this situation a couple of times and on both occasions it was shared or 'borrowed' neutrals that needed to be separated, both times between two lighting circuits.
Now I try to do a quick continuity check between neutral conductors before re-wiring a new CU (don't always remember though)
Thanks to all for your comments.
Have been back today to progress.
Further testing and check neutrals etc gave me the following.
9 circuits -
x 4 for lights, old rubber cable with no earth on any. All insulation tests L/N good, no cotinuity with neutrals and managed to get all 4 on RCD working. Although a lot of metal fittings.
x 1 Shower on t/e red black. All insulation values good and ok now on RCD.
X 3 Socket circuits all with earth on rubber sheathed cables trip RCD and insulation values ok except L/N on 1 circuit.
x 1 oven circuit with earth on rubber sheathed cable trips RCD. Insulation value failed on N/E
the fittings will have to come down if theirs no earth to them, Ive just done a consumer unit change in a block of ex council flats, Had the same problems, lets just say i feel 10 years older!
just what i've told customer. However,
not happy and don't think there going to comply. Will note my advice on cert and label consumer unit. Done a few jobs here and funny how customer always says she wants to.move when i've been. Cheaper to rewire i think.