730kVA generator: 3x 240mm single core cable (per phase + neutral = 12 single cores in total)

Phase 1 - on generator display panel it shows load to be 600 amps. However, when i put my clamp on ammeter onto the single cores of each of the singles for this phase I get one core with 350 amps, another with 100 amps and the last one with 150 amps (give or take oddities here and there) I know this adds upto 600 amps...........but why is the current not evenly spread across the 3 cores????

It is important to state that the length of the 'tails' are all the same, the cable type is the same and the connections are all torqued and clean.

I have spoke with a generator tech and he said he has experienced the same, yet didn't know why...............just like me.

Any answers appreciated.
 
Are the temperatures of the 3 tails the same?

Is this a permanently wired in Genny or temporary with flexible connections?
 
Well it's a bit difficult to tell really..................because its very hot where i am. The gen is permanent, with the singles going out of the gen panel into a cable tray that goes down through a concrete trench for approx 5 metres and then back up out of the ground in cable tray to a control room panel.

There are some bends in the routing, but nothing to get excited about......................oh, the cables are in trefoil formation in the cable tray also. I heard somewhere about the skin effect and wondered if it may be similiar sort of thing. However, don't know enough about it to positively say 'Yes' or 'No'??
 
Can't say i've experienced your query myself, but the trifoil arrangement is the correct method of transporting these conductors, I take it that your trifoil arrangement consists of all 3 phases and not same phase trifoil arrangement??
 
Yes, the phases are grouped together in trefoil. And then the 3 neutrals and 2 x 120mm earthing conductors are grouped separately about 6 inches to the side.

It seemed strange to me, and i was concerned that the current carrying capacity of the cables will be exceeded by this...............It is the same for all the phases i might add.........not just L1.
 
Any chance of taking some photo's of the connections at each end of this installation?? Do you know if these cables were trifoiled before they were pulled into the trench on this tray work (i'm taking it you can't see these cables run's after they go below ground). I've seen some real lash-ups where cables disappear for part of the cable run, all looks good where they are seen and are accessible, but a complete mess where they aren't accessible and can't be seen...

Also how are these single cores existing/entering the metal enclosures, hopefully not through single holes per core, unless an insulating plate has been used to stop circulating currents??...
 
Last edited by a moderator:
I'm sure there's some magical effect that when 1 cable gets close to it's carrying limit, or is about to melt, the load increases on the less loaded cables.
Can't back it up tho!!
 
I have photos actually yes, they were installed by our sub contractors. I will dig them out and send them to you.

The cable are not in trefoil formation for about ............4ft when they come out of the control panel as it would have been a nightmare to arrange them in such a way and then get them into the designated busbar connections (240mm remember).

The cables are in nice and neat, we QAQC'd them prior to them getting covered up. So i can safely say i'm happy with that side of things.

The glands into the control panel are PVC compression glands (cable is not armoured).............and we had to modify the panel and use non-ferrous plate (aluminium) where they terminate to avoid the effects of eddy currents etc etc.

I will dig the photos out, thank you.
 
I have photos actually yes, they were installed by our sub contractors. I will dig them out and send them to you.

The cable are not in trefoil formation for about ............4ft when they come out of the control panel as it would have been a nightmare to arrange them in such a way and then get them into the designated busbar connections (240mm remember).

The cables are in nice and neat, we QAQC'd them prior to them getting covered up. So i can safely say i'm happy with that side of things.

The glands into the control panel are PVC compression glands (cable is not armoured).............and we had to modify the panel and use non-ferrous plate (aluminium) where they terminate to avoid the effects of eddy currents etc etc.

I will dig the photos out, thank you.

OK, fair enough with the cable installation. That's normal to have an arrangement/dressing space of a round a metre or so, on multi core parallel cable runs on Tray. I didn't think for a moment that the single cores were armoured...lol!!!

From experience Aluminium plate is only any good for stopping circulating currents up to around 250/300A, It reduces rather than eliminates circulating currents. Which is why i always throw away supplied Aluminium gland plates on Switchboards and MDB's where being fed by multi single core cables etc, and replace with 10mm insulating board plates. Are the cables insulation getting very warm to hot around these aluminium plates??
 
Personally I’d be getting a Ductor on the tails to check the balance. Doesn’t take much to throw them out of balance.
 
That's interesting you mention about the Aluminium plate. Well the ambient temperature here is 50 degrees at times so it's difficult to gauge..........I wouldn't say they were unusually hot.

Is it safe for me to assume that this occurence is out of the ordinary and there might be something not quite right? With the other gen tech saying he had witnessed the same, I was hoping someone could baffle me with science to put my mind at ease?

Could you enlighten me on the experience with regard to the aluminium plates? This interests me.

Thanks
 