Hobsoni
730kVA generator: 3x 240mm single core cable (per phase + neutral = 12 single cores in total)
Phase 1 - on generator display panel it shows load to be 600 amps. However, when i put my clamp on ammeter onto the single cores of each of the singles for this phase I get one core with 350 amps, another with 100 amps and the last one with 150 amps (give or take oddities here and there) I know this adds upto 600 amps...........but why is the current not evenly spread across the 3 cores????
It is important to state that the length of the 'tails' are all the same, the cable type is the same and the connections are all torqued and clean.
I have spoke with a generator tech and he said he has experienced the same, yet didn't know why...............just like me.
Any answers appreciated.
Phase 1 - on generator display panel it shows load to be 600 amps. However, when i put my clamp on ammeter onto the single cores of each of the singles for this phase I get one core with 350 amps, another with 100 amps and the last one with 150 amps (give or take oddities here and there) I know this adds upto 600 amps...........but why is the current not evenly spread across the 3 cores????