That last post makes more sense if you read the whole section. But does that mean if you show them your qualifications they'll let you test the job anyway?
Certification by a building control body
3.8 If an installer is not a registered competent person and has not appointed a registered third-party certifier, then before work begins the installer must notify a building control body.
3.9 The building control body will determine the extent of inspection and testing needed for it to establish that the work is safe, based on the nature of the electrical work and the competence
of the installer. The building control body may choose to carry out any necessary inspection and testing itself, or it may contract a specialist to carry out some or all of the work and furnish it with an electrical installation condition report.
3.10 An installer who is competent to carry out inspection and testing should give the appropriate
BS 7671 certificate to the building control body, who will then take the certificate and the installer’s qualifications into account in deciding what further action, if any, it needs to take. Building control bodies may ask installers for evidence of their qualifications.
3.11 This can result in a lower building control charge as, when setting its charge, a local authority is required by the Building (Local Authority Charges) Regulations 2010 to take account of the amount of inspection work that it considers it will need to carry out.
3.12 Once the building control body has decided that, as far as can be ascertained, the work meets all Building Regulations requirements, it will issue to the occupier a Building Regulations completion certificate (if a local authority) or a final certificate (if an approved inspector).
Certification by a building control body
3.8 If an installer is not a registered competent person and has not appointed a registered third-party certifier, then before work begins the installer must notify a building control body.
3.9 The building control body will determine the extent of inspection and testing needed for it to establish that the work is safe, based on the nature of the electrical work and the competence
of the installer. The building control body may choose to carry out any necessary inspection and testing itself, or it may contract a specialist to carry out some or all of the work and furnish it with an electrical installation condition report.
3.10 An installer who is competent to carry out inspection and testing should give the appropriate
BS 7671 certificate to the building control body, who will then take the certificate and the installer’s qualifications into account in deciding what further action, if any, it needs to take. Building control bodies may ask installers for evidence of their qualifications.
3.11 This can result in a lower building control charge as, when setting its charge, a local authority is required by the Building (Local Authority Charges) Regulations 2010 to take account of the amount of inspection work that it considers it will need to carry out.
3.12 Once the building control body has decided that, as far as can be ascertained, the work meets all Building Regulations requirements, it will issue to the occupier a Building Regulations completion certificate (if a local authority) or a final certificate (if an approved inspector).