Quick question, just wanted to see what others think about this.

Working on a job at the moment in offices, wiring and connecting sockets in dado trunking.

Was pulled-up today for connecting the two earth cables in the same terminal on the back of the dual socket.
Was told that each earth should be doubled back and terminated in individual earth terminals on the back of the socket. (MK sockets with dual earth)

However when i had a look at the back of the socket, the two earth terminals are joined together anyway.
Didnt want to question his knowledge but just thought it was a bit 'picky'

Was i just being 'put in my place' or is there a reg regarding this? Cant seem to find anything myself.

Anyone got any thoughts?
 
I would say they were correct as this circuit could very well be designed with 'high integrity' earthing.
 
Quick question, just wanted to see what others think about this.

Working on a job at the moment in offices, wiring and connecting sockets in dado trunking.

Was pulled-up today for connecting the two earth cables in the same terminal on the back of the dual socket.
Was told that each earth should be doubled back and terminated in individual earth terminals on the back of the socket. (MK sockets with dual earth)

However when i had a look at the back of the socket, the two earth terminals are joined together anyway.
Didnt want to question his knowledge but just thought it was a bit 'picky'

Was i just being 'put in my place' or is there a reg regarding this? Cant seem to find anything myself.

Anyone got any thoughts?


More than likely high integrity earthing as it is in an office. ie split cpc's at sockets and cu / db.

Is it a ring or a radial circuit?
 
Last edited by a moderator:
607-02-05 Where two protective conductors are used in accordance with Regulation 607-02-04 (iii), the ends of the protective conductors shall be terminated independently of each other at all connection points throughout the circuit. e.g. the distribution board, junction boxes and socket-outlets. This requires an accessory to be provided with two separate earth terminals.

Ah ha!

More than likely high integrity earthing as it is in an office. ie split cpc's at sockets and cu / db.

Is it a ring or a radial circuit?


Ring, wired in 4mm T+E
 
Last edited by a moderator:
Come on then, who is going to explain why?

:D:D:D:D


Go on then! ;)

The only thing i thought of, was if one earth terminal became loose you would still have the other giving continuity throughout the circuit
 
Last edited by a moderator:
Go on then! ;)
The only thing i thought of, was if one earth terminal became loose you would still have the other giving continuity throughout the circuit


Top of the class!!!! (nearly)

It ensures that the socket outlet still has a cpc connected

:D
 
Tidy!

Ive found on the net about high integrity earthing needed on items with high earth leakage, so IT equipment right?

You really do learn something everyday!
 
It is in the regs--- somewhere.

A lot of office blocks and office refurbs etc should now be installed this way.

Ill see if i can find it.

Edit Found --- 543.7.1.4


Not sure where you got your reg number from:confused:
 
Last edited by a moderator: