Aaronj46

Regular EF Member
So I have been working on a contract installing 10.5kw showers with B40 MCB's as specified by builders but occasionally a plot reports the shower tripping when having long showers. Hager don't do a 45A MCB but do a 45A RCBO but then its the cost....£££

The cable is ran in uninsulated studwork for around 9metres to the isolator and then around 4metres to go into loft and back down. Is there a way a I can justify a B50?

Any suggestions would be much appreciated!
 

Taylortwocities

Electrician's Arms
CCTV / Alarms
What do your cable calculations say about having a B50 on the 10mm cable, given the installation method?
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
who in their right mind wants a long shower? in, wet, soap, rinse, out for some beer. 5 minutes tops.
 

Spoon

Forum Mentor
Electrician's Arms
CCTV / Alarms
Trainee Access
DIY
I'm with Post #2...
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
I,m with RBS.
 

Andy78

Respected Member
Forum Mentor
Electrician's Arms
Trainee Access
So I have been working on a contract installing 10.5kw showers with B40 MCB's as specified by builders but occasionally a plot reports the shower tripping when having long showers. Hager don't do a 45A MCB but do a 45A RCBO but then its the cost....£££

The cable is ran in uninsulated studwork for around 9metres to the isolator and then around 4metres to go into loft and back down. Is there a way a I can justify a B50?

Any suggestions would be much appreciated!
Cost ? £20 to do the job properly ?

No idea as only you know the routes and installation methods and the derating factors involved.
 

Spoon

Forum Mentor
Electrician's Arms
CCTV / Alarms
Trainee Access
DIY
My 16 YO daughter, for one. the Megaflo is 210 litres, but she can run it cold......:mad::mad::mad:
Disconnect shower and tell her to have a bath... that will save you a bit.
 

essex

Forum Mentor
Electrician's Arms
Trainee Access
Shower room circuits should have RCD protection anyway.
 

Pete999

Forum Mentor
Electrician's Arms
Trainee Access
who in their right mind wants a long shower? in, wet, soap, rinse, out for some beer. 5 minutes tops.
Turn it on, run about for a bit you won't need a towel then, the builder specified the MCB let him sort it Mate, Although wonder how much he knows about electrics, probably specified from memory, oh that's what most shower installs consist of.
 

Spoon

Forum Mentor
Electrician's Arms
CCTV / Alarms
Trainee Access
DIY
Turn it on, run about for a bit you won't need a towel then
What are you doing??????? I now have an image of you all wet, running around naked.... I need a 'Delete' button....
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
What are you doing??????? I now have an image of you all wet, running around naked.... I need a 'Delete' button....
just send him an invite to survey the nursing home.:D:D:D.
 

Wilko

Electrician's Arms
Hi - what size are the conductors? If you're using 6mm then 50A is a definite no. If there's no faults, I'd replace the mcb and see if it stops tripping.
 

Electrician Talk

Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.