Phil I swear I just saw your bit about a fundamental error and I said "10800kw for starter"
No idea where the post has gone
Update
That ones in the arms Dammit:)
 
Example of reg 433.3.1 (ii).. would be fitting a 2way board with 2 x 16a mcb's you could effectively feed board of an Henley block in 6mm tails regardless of how large the fuse up-stream was because it cant draw long term a load exceeding the value of both mcb's.
This is like what was know as the busbar rule, with the reverse fusing. As far as i know its still acceptable as long as the fault protection covers upstream supply. But its one of the old school methods and would not be concidered by most now.
 
This is like what was know as the busbar rule, with the reverse fusing. As far as i know its still acceptable as long as the fault protection covers upstream supply. But its one of the old school methods and would not be concidered by most now.

Still see it alot, have you tried getting 25mm tails into a 2way board lol, but yes im currently fitting isolators of a 200amp busbar with tails from 16mm to 70mm coming off it into switchfuses.. waste of copper and money otherwise.
 
Well.....Bottoms to you all, I have a 10.8Kw shower at home and I installed it on the 40A 10mm circuit..............................

Its fine!

No melted cables, no house fire.

HOWEVER>>>> Would I do this at a clients house Hmmmmm?

Can you imagine trying to install 16mm T+E into an MK shower isolator?????
 
I agree with what was stated on the IET Forum to you, which is that Clipped Direct (C) is by far and away the most common reference method in a domestic installation. Also, as said, the shower is a fixed load which cannot overload and so the protective device need only provide fault protection.

but that would mean there no insulation in the property, and most if not all new builds have insulation in them so i can't see how it would b ref method c
 
I was surprised to see the other day a shower isolator light switch! I couldn't find a shower isolator so a search in the loft above revealed a 16mm cable to a sub board, with a double pole contactor as the isolator, switched by a light switch on the outside of the bathroom. This was a recently installed 10.8kw shower carried out by a bathroom company. So there's your answer, 16mm cable, contactor, rewire, rebuild etc!
 
DS, if you’re that worried about it put a 16mm in. Two forums have advised you, but you seem unwilling / incapable of taking advise.
Do it your own way!
 
10mm on a 50Amp breaker it is.

just wanted to be comfortable in understanding it so i can explain myself if I have to.

Thank you very much all
 
but that would mean there no insulation in the property, and most if not all new builds have insulation in them so i can't see how it would b ref method c

Rather than derating it's generally better to avoid the insulation! No reason why in almost all cases you shouldn't be able to prevent it being a factor.
 
If you have 400mm of 2/2 trunking fitted vertically where it passes through the insulation you really dont need to apply methods related to cable in trunking.... the trunking is open top and several orders larger than the cable so any thermal dissipation restrictions will be neglegible and clipped direct can be used as normal.
 

Reply to 10.8kW shower cable size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, Same project as detailed in my other post (I want to run shower cables to the CU whilst the kitchen ceiling is disturbed). I'm going to...
Replies
5
Views
3K
Hey all, Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs...
Replies
3
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
421
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock