Discuss 10 Bedroom house rewire. Ring or radial? in the UK Electrical Forum area at ElectriciansForums.net

Moaz

-
Reaction score
8
Guys, I'm wiring a ten bedroom house which has 4 floors. Correct me if I'm wrong, but as fat as I know, new regs says to keep each room on a radial. So shall I keep each room on a radial or have a few rings on each floor after calculating the maximum demand??
 
i havent even started reading up on the 18th yet, is this going to be a thing?

how will adding into a rfc work with this set up if its true after the 18th comes out? would you have to run a radial from board for 1 extra socket?
 
Best you look at the calculations
... Where is the CU going to be?

Volt drop springs to mind

You haven't been reading the French regs have you?

Lol no!! I've allowed for a CU on each floor. Very big house! It'll save me alot of time and money running a few legs back to the CU to make it in to a ring. I might just wire them as radials.
 
Is that actually coming into force? Radial per room? That’s a joke.

Best idea ever. (If it's true). You are not looking at this correctly.
If the kids are not doing as they are told or spending too much time on their console you can isolate their room without affecting any other rooms. Everyone happy... Except for the kid who isn't doing as they are told..
 
Best idea ever. (If it's true). You are not looking at this correctly.
If the kids are not doing as they are told or spending too much time on their console you can isolate their room without affecting any other rooms. Everyone happy... Except for the kid who isn't doing as they are told..
thats a bit fritzl
 
Lol no!! I've allowed for a CU on each floor. Very big house! It'll save me alot of time and money running a few legs back to the CU to make it in to a ring. I might just wire them as radials.
What about the other circuits, lighting etc if it's a HMO?
 
Best idea ever. (If it's true). You are not looking at this correctly.
If the kids are not doing as they are told or spending too much time on their console you can isolate their room without affecting any other rooms. Everyone happy... Except for the kid who isn't doing as they are told..

Plus, all the circuits will be on rcbos so it's a win win.
 
Is it a HMO dwelling? Ah right see you have answered that question in the above post. Came through as I sent the question sorry Moaz
 
Yeh right calculate earth leakage! Also longevity of cable and who will be using it throughout it's life and how many times per day subject turning on and turning off, no problemo!
 
Anyway Moaz wire it how you like. You know the property and it's layout.

Just be aware of you cable lengths and do your calcs...and you may need to do 4mm radials if the property is that big..

R1+Rn (which you can get from Onsite guide)multipled by the rating of fuse you want to use multipled by the correction factor of 1.2 (70c)

Simple job done.
 
Anyway Moaz wire it how you like. You know the property and it's layout.

Just be aware of you cable lengths and do your calcs...and you may need to do 4mm radials if the property is that big..

R1+Rn (which you can get from Onsite guide)multipled by the rating of fuse you want to use multipled by the correction factor of 1.2 (70c)

Simple job done.
not if there are seperate CU's on each floor, depends how big the "floor" is though, it might be 10 small box rooms or david camerons house
 
Surely if the implementation of arc protective devices is imminent this would be another reason to use radial circuits...??
 
not if there are seperate CU's on each floor, depends how big the "floor" is though, it might be 10 small box rooms or david camerons house

Your right it could be very small :) but the OP is the one who's been there
I think Moaz said it was large, he didn't say if the DB on each floor was at the middle or the end of the house. So who knows how long the radial could end up being.
 
Why a hot potato?

Because they need to be licenced / registered with the local authorities, inspected and subject to more stringent tests etc than a normal domestic property.

A single room in my patch (in a scruffy area) can easily be "worth" £500 per month, so convert the lounge and dining room and hey presto a 3 bed house is now a 5 bed HMO - so £2500 per month or £30,000 per year .....

Then there are cash payments and loss of tax revenues

I could go on
 
Because they need to be licenced / registered with the local authorities, inspected and subject to more stringent tests etc than a normal domestic property.

A single room in my patch (in a scruffy area) can easily be "worth" £500 per month, so convert the lounge and dining room and hey presto a 3 bed house is now a 5 bed HMO - so £2500 per month or £30,000 per year .....

Then there are cash payments and loss of tax revenues

I could go on
we had a landlord try convert their 3 bed house to a hmo, they didnt split the ring upstairs where all the rooms are though lol, still it will be something for the tenants to fight over when the bill comes in
 
Guys, I'm wiring a ten bedroom house which has 4 floors. Correct me if I'm wrong, but as fat as I know, new regs says to keep each room on a radial. So shall I keep each room on a radial or have a few rings on each floor after calculating the maximum demand??
What new reg it that? what reg are you referring to that gives you that impression? however, if that is the/your design there is nothing wrong with it it is in my view a bit OTT unless there is more to this house than a family house.
 
Because they need to be licenced / registered with the local authorities, inspected and subject to more stringent tests etc than a normal domestic property........
Do they have specific extra requirements on the electrical side?
 
Do they have specific extra requirements on the electrical side?
I don't know about "requirements" but I've just rewired a house which is being turned into an HMO - they wanted the fire detection to comply with LD1, emergency lighting on the escape route and in the lounge and kitchen, and for some reason the lighting in those areas permanently on.
 
we had a landlord try convert their 3 bed house to a hmo, they didnt split the ring upstairs where all the rooms are though lol, still it will be something for the tenants to fight over when the bill comes in

Why .......... if the tenancy agreement says the bills will be split evenly , then evenly split they will be..............

There is no requirement for separate circuits in bedrooms AFAIAA
 
Does the fire detection equipment and emergency lighting fall under the 7671 electrical installation regs or under building regs?
 

Reply to 10 Bedroom house rewire. Ring or radial? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
768
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
869
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
928
Hi all, I posted here some time ago asking for validation of a quote I received for a rewire. (10k assumed 60 points) And got some good advice so...
Replies
2
Views
595
Hello. Homeowner trying to understand what is a fair quote for full rewire. We've had to tear the ceilings down as part of unplanned asbestos...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock