Hi all
I am in an industrial unit and the 100mA RCCB keeps tripping.
They use it as the main switch inside of the unit's distribution board. The mainboard that feeds all the units has an MCB in it.
The RCCB keeps tripping when I plug-in AC to DC transformer loads such as laptops, speakers, monitors etc.
The 30mA RCBO that does the sockets (and my lights in my office) does not trip.
And I don't have all of these devices plugged in at the same time. Right now my laptop is plugged in with the other office equipment, but my monitors and speakers are not. If I plug those in, it trips. If I put any load on my constant current/voltage DC power supply, it trips. Talking less than 1w and it trips.
I have already replaced it with another RCCB of the same make and model just to see if the old one is faulty but it does the same thing.
When I swapped the RCCB over, it tripped as soon as I connected it back up to the board. The MCB was off, though it was only a 3 pole...
It also trips randomly when everything has been fine for hours. Not much if anything connected and it will just trip.
Every night it trips.
Any ideas on what I can do? What tests can I do?
I am thinking it is a natural leaking to earth somewhere? I should check between ground and neutral on the incoming supply and within my unit?
Thanks
Jack
(yes I am aware that I should get an electrical in, the site electrician was meant to be on site last week but never showed and I will be getting my personal electrical in next week or so when they can book me in)
I am in an industrial unit and the 100mA RCCB keeps tripping.
They use it as the main switch inside of the unit's distribution board. The mainboard that feeds all the units has an MCB in it.
The RCCB keeps tripping when I plug-in AC to DC transformer loads such as laptops, speakers, monitors etc.
The 30mA RCBO that does the sockets (and my lights in my office) does not trip.
And I don't have all of these devices plugged in at the same time. Right now my laptop is plugged in with the other office equipment, but my monitors and speakers are not. If I plug those in, it trips. If I put any load on my constant current/voltage DC power supply, it trips. Talking less than 1w and it trips.
I have already replaced it with another RCCB of the same make and model just to see if the old one is faulty but it does the same thing.
When I swapped the RCCB over, it tripped as soon as I connected it back up to the board. The MCB was off, though it was only a 3 pole...
It also trips randomly when everything has been fine for hours. Not much if anything connected and it will just trip.
Every night it trips.
Any ideas on what I can do? What tests can I do?
I am thinking it is a natural leaking to earth somewhere? I should check between ground and neutral on the incoming supply and within my unit?
Thanks
Jack
(yes I am aware that I should get an electrical in, the site electrician was meant to be on site last week but never showed and I will be getting my personal electrical in next week or so when they can book me in)