S
sparksburnout
Can I just ask, why are some guys speccing SWA when it is within the confines of a domestic dwelling??? Are we anticipating the occupants to be trying to dig the place up?
Oops:lipsrsealed2:
Hey thats why Im banned from texting especially when trying to get into some women's ........
So just out of interest, and I am by no means fluent in this aspect, but, Im led to believe that discrimination or even partial discrimination is not possible between MCB and MCB.
No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???It depends entirely on the prospective fault current. Discrimination for the purpose of overload protection is entirely affordable though.
- - - Updated - - -
Because that's what the OP said the customer asked for.
Are you happy to bury a non-RCD protected T+E submain in the wall then?
Yes overload I understand, but with short circuit its more complicated. I thought cascading/discrimination was usually in the ratio 2:1 with fuses or perhaps a mixture of fuses and MCBs. Although I've read that you need the downstream device to have a total I2t less than the pre arcing I2t of the upstream device, I've yet to get round to fully grasping this aspect and to be honest have never been in a situation where I've need the knowledge. Perhaps I need to read up on this and maybe start a new thread.:smile5:
Loads of switch fuses and henly block dont like the sound of that,, one main switch to isolate the Complete supply then one decent TP CU with single phase conversion kit , with a circuit supplying each Flat, if its a new install the i would use a 3 core swa and use 16mm reason for this is if they decide to up grade the flats in the future then the supplies are there , always plan for the future
I must check my supplier then, that seems mad!!An RCD up front and then another in the board?! Ah yes good point, each room would have to have it's own RCD or it would take out the whole lot. Could you not use a 100mA time delay RCD in a CU after the meter, and then 30mA in each individual CU, that way protecting the T&E?
Dunno where you get your SWA from but I get it cheaper that T+E.
And you've just priced yourself out of the work!![]()
No, I didn't make myself very clear I admit. I was initially suggesting only one RCD in a CU that would then feed each individual CU, but I now realise after giving it more than 10 secs thought that this would be crap. However, could you not use the method i suggested in my reply to D Skelton? I was not advocating having a buried T&E with no RCD protection!Can you explain what you actually mean? So are you saying put a front end 30mA RCD on each supply to each flat with T&E submain burried?