I couldnt agree more, cost is important and would be the difference winning or loosing the job, but to be honest I've got no idea what HMOs are...her majestics office? Her majesties orders??? Himmlers marching orders??
I suppose HRC fuse carriers in a metal clad main board would be cheaper than a number of switched fuses.
Just re-use an old one and repair any damage to the original enclosure. Im sure most are still good for another 20 or so years service.
Ok. The set up his current electrician has is as follows
single phase TNS 100A BS1361. Tails into single meter.
From there into Henley blocks using 25mm tails.
From Henley blocks, 25mm tails into Mk60A isolator.
From isolator 10mm T&E ( presume buried in wall & under floor etc into consumer unit.
Consumer unit has 30ma RCD main switch and 2 circuits. Lights and sockets.
I also would have though swa from isolator into consumer unit.
But I would use 16mm ??
bonding as far as I could see is main gas and water in 10mm. I couldn't see an earth from the metal isolators to the MET though. Also couldn't see any supplementary bonding in the rooms. That's why the alarm bells rang in the head.
But I don't think 10mm T&E is the way to go ?
Sav
I don't tend to keep old gear that I rip out, let alone sell it lol.
I stand by what I say. MCB's up front. Without that you're looking at 5 x switchfuses, 5 x 45A HRCs, 6mm SWA cable and a lot of bother.
The fact remains, the installation of MCBs up front is perfectly compliant and gives more than adequate discrimination for overload purposes. In the unlikely even of a short circuit on a brand new installation, then the main DB would just have to remain accessible wouldn't it.
Spec switchfuses, lose the work, it's really that simple.
Hey I like the selective quote...makes me look a bit rogue'ish...so tell me why suddenly on the attact? its all opinion if compliant to BS7671 or some other suitable Regulation
Oops:lipsrsealed2:
Hey thats why Im banned from texting especially when trying to get into some women's ........
So just out of interest, and I am by no means fluent in this aspect, but, Im led to believe that discrimination or even partial discrimination is not possible between MCB and MCB.
Can I just ask, why are some guys speccing SWA when it is within the confines of a domestic dwelling??? Are we anticipating the occupants to be trying to dig the place up?
No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???It depends entirely on the prospective fault current. Discrimination for the purpose of overload protection is entirely affordable though.
- - - Updated - - -
Because that's what the OP said the customer asked for.
Are you happy to bury a non-RCD protected T+E submain in the wall then?
No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???
No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???
Yes overload I understand, but with short circuit its more complicated. I thought cascading/discrimination was usually in the ratio 2:1 with fuses or perhaps a mixture of fuses and MCBs. Although I've read that you need the downstream device to have a total I2t less than the pre arcing I2t of the upstream device, I've yet to get round to fully grasping this aspect and to be honest have never been in a situation where I've need the knowledge. Perhaps I need to read up on this and maybe start a new thread.:smile5:
Loads of switch fuses and henly block dont like the sound of that,, one main switch to isolate the Complete supply then one decent TP CU with single phase conversion kit , with a circuit supplying each Flat, if its a new install the i would use a 3 core swa and use 16mm reason for this is if they decide to up grade the flats in the future then the supplies are there , always plan for the future