Currently reading:
11-12 volts reading across line and earth
Discuss 11-12 volts reading across line and earth in the UK Electrical Forum area at ElectriciansForums.net
Sting Ray
trying to trace an earth fault in a friends home today after the RCD in the single ring main suddenly and persistently started tripping
why might I see 11 to 12 volts across line and earth on some sockets?
are there any tips regarding finding the earth fault? have broken the ring and disconnected all sockets and i am working my way along the ring reconnecting one socket at a time until the fault reappears
Is this with the circuit live or isolated?
Have you got a mega tester?
To restate:
I see 11 to 12 volts across line and earth and a very low insulation resistance at 500V test voltage between line and earth
I know there is a short circuit somewhere and I have cleared all but two outlets on the ring so the ring is presently configured as a radial with the last part of the ring dead ie not connected to the main board or the incoming ring cable
I was curious about why the 11 to 12 volts appeared, nothing else
... why might I see 11 to 12 volts across line and earth on some sockets?
To restate:
I know there is a short circuit somewhere...
Okay the way I read this is you're actually worrying about two different faults here. Firstly there's the low insulation that was causing the RCD to trip. Secondly there's a mysterious 11-12 volts appearing at some sockets between the L and E.
Just ignore the 11-12 volts between the L&E, chances are it's a meaningless reading because you're using a tester with an extremely high input impedance which is over sensitive. Concentrate on finding the extremely low insulation problem between N and E.
Start the fault finding technique either loose cable or damaged cable by screw etc break the ring main down until you find it.
Good luck can be a full in gruler it you could get lucky,
I once found that after British gas had put some pipes in the ring main randomly tripped turns out they had snagged a cable with the new nails they out in to floor boards and if some one walked on them it would trip too ages find can't beat the best in the business
Where has this trend for measuring voltage to do fault finding come from ?
I have noticed quite a lot of fault finding questions being posted, real,induced and phantom voltages are noted, then used to try and trace insulation and continuity problems
Does the training reflect this method these days or is it just the "in" thing to do this
Just to close this one, fault traced to part of ring next to boiler, cables buried in wall and also in inaccessible ceiling void. Broke ring at nearest reasonable point and remade ring with those lovely Wago connectors, like taking out a bit of bowel. All good except boiler now needs new permanent supply rather than the extension lead from a nearby socket. Also found many sockets with green goo, I know what that is now but the client doesn't want to consider a rewire just yet. Ring is a ring, insulation >999MOhms, happy days. Thanks
No idea, but switching off other circuits normally clears it!
Just to close this one, ........ insulation >999MOhms, happy days. Thanks
Glad to hear you got it sorted out.
I was also thinking the same thing a few days ago. It's a poor way to localise a fault and it causes a lot of confusion with the digital testers nowadays which are way over-sensitive. I hope to hell they're not teaching this method on the courses.
I'm surprised how few sparkies carry an analogue voltmeter nowadays, I'd say it's as much an essential piece of kit as it ever was. Digital testers are great for some things but the fact they're way over sensitive for many general applications coupled with the lack of understanding of how attributes such as their input impedance and burden affects the results you see and regularly causes chaos.
Reply to 11-12 volts reading across line and earth in the UK Electrical Forum area at ElectriciansForums.net