You do not need to state the regulation number on a eicr but yes the code does have to relate to something meaningful in the regulations that gives rise to possible danger and safety issues of the existing installation
but Iz is the current capacity of the cable, not related to the socket.It would seam he has fallen into the trap of Ib<In<Iz which is really only applicable if overload is a factor.
As this is a fixed load then he can't code it based on this alone.
Yeah but perhaps he's thinking of the flex that plugs into the socket if it's only 1.5mm2but Iz is the current capacity of the cable, not related to the socket.