16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

Discuss 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers
 
It would seam he has fallen into the trap of Ib<In<Iz which is really only applicable if overload is a factor.
As this is a fixed load then he can't code it based on this alone.
but Iz is the current capacity of the cable, not related to the socket.
 
Exactly and when I question what reg they are coding it under I've heard nothing?
regulation 000.00.000. thou shalt not code anything that does not contravene any of the other regulations that we, the all knowing, all seeing, IET, want to dream up to make electricians lives more difficult than we have already made them. ..........


......... excuse the break. amendments to the 18th neeed to be drafted.

these will, of course incur charges at you normal rates.
 
It would seam he has fallen into the trap of Ib<In<Iz which is really only applicable if overload is a factor.
As this is a fixed load then he can't code it based on this alone.

It's a bit of a stretch to call a socket outlet a fixed load isn't it?

And the fact that when connected via a 16A mcb it trips on overload it suggests that the 16A socket is overloaded.
 
You have had your work queried during a subsequent inspection.
You know that the situation is not contravening the wiring regulations and the inspector cannot provide a regulation to match the C2 coding.
Advise the customer of this and finish the discussion.
Unless anything further comes up there is nothing to pursue.

You can consider the merits of the comparison of the protective device and the rating of an accessory but that is not really an issue in this case despite what you have mentioned about the loading and MCB operation. So long as the socket is not taking more than 16A then there is no problem.
 

Reply to 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top