Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers
 
Exactly and when I question what reg they are coding it under I've heard nothing?
regulation 000.00.000. thou shalt not code anything that does not contravene any of the other regulations that we, the all knowing, all seeing, IET, want to dream up to make electricians lives more difficult than we have already made them. ..........


......... excuse the break. amendments to the 18th neeed to be drafted.

these will, of course incur charges at you normal rates.
 
It would seam he has fallen into the trap of Ib<In<Iz which is really only applicable if overload is a factor.
As this is a fixed load then he can't code it based on this alone.

It's a bit of a stretch to call a socket outlet a fixed load isn't it?

And the fact that when connected via a 16A mcb it trips on overload it suggests that the 16A socket is overloaded.
 
I've lost track dave, I thought this thread was about coding something incorrectly, then it's went to overloaded 16 amp socket.

It started out that way, but then the OP revealed that the reason he fitted a 20A ocpd was that the load causes a 16A ocpd to trip on overload.
 
You have had your work queried during a subsequent inspection.
You know that the situation is not contravening the wiring regulations and the inspector cannot provide a regulation to match the C2 coding.
Advise the customer of this and finish the discussion.
Unless anything further comes up there is nothing to pursue.

You can consider the merits of the comparison of the protective device and the rating of an accessory but that is not really an issue in this case despite what you have mentioned about the loading and MCB operation. So long as the socket is not taking more than 16A then there is no problem.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester

Thread Information

Title
16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
66
Unsolved
--

Advert

Thread statistics

Created
David Rann,
Last reply from
David Rann,
Replies
66
Views
21,889

Advert

Back
Top