Afternoon everyone, I've just been to a neighbours house who has just her home completely done up as the foundations are shot. The house has been rewired and in doing so the consumer unit has been moved to one side of the house (the main fuse is outside on the other side of house). I've gone to swap a light fitting over for her and have noticed the elec contractor who's rewired it has used 16mm t&e supply. The cable is buried within the wall so not sure what protection they've used, i might dig out some of the plaster to see. The main fuse is an 80A (the seal has been cut off the fuse carrier so i checked). There are 1 x 10mm for shower, 1 x 10mm for cooker, 1 x 10mm for hob, 3 x ring circuits, 1 x radial and 3 x lighting circuits. The job must have been signed off already and I haven't done any cable calcs yet but it just doesn't sit right with me. Has anyone came across this before? Opinions? Thanks in advance.

Ste
 
How far does the cable run, how is it installed, has it been given circuit protection, where are the main protective bonds connected.
 
It has been rewired within the last 6 months. The cable run must be 15m give or take, bonding comes from the main earth block at meter cupboard, no RCD on the 16mm T&E though (sorry was meant to say that), it's wired into a separate DP iso, i think 100A but will double check.
 
So have they provided circuit protection or are they relying on the service head fuse.
 
A quick referral to table 4D5, suggests the best ccc for 16mm tw&e is 85a (clipped direct). So with 15m negotiating through the house, can't see how its ever going to suffice? And as it buried in a wall, chances are without earthed steel plate capping, its going to need additional protection

Seen it may a time mind.
 
How is the T&E connected at the origin? Because the way I'm picturing it there will be non-sheathed conductors outside of any enclosure or containment at that point.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16mm T&E to Consumer Unit
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
46

Advert

Thread statistics

Created
hogey,
Last reply from
chris day,
Replies
46
Views
17,717

Advert

Back
Top