Doing an EICR on a property and came to the kitchen, when i dropped the sockets my jaw also dropped, no end to end on the ring, one socket had the following spurred off of it - 3 double sockets, extractor hood, cooker ignition which then also had another socket spurred off that to feed a washing machine!!!! dropped another socket as looking for other leg of the ring to find a socket fed in 1.5mm!!! The guy has just had his kitchen fitted, looks all lovely and nice on the surface but really bad underneith. This was done by a Romanian builder who has no clue re electrics. I told the guy this needs to be sorted asap, i suggested he'll need a few fcus for the various spurs but it'll mean breaking a tile or two to put them in, cant really put any sockets below as cupboards already fitted, then try to find the other leg and put links between to make a complete ring, cant see any other way of doing it other then putting it on a 20A radial but that's not an ideal solution in my mind really, any other ideas? I thought you could only spur once off a socket unless you put an fcu then you can have as many as you like, didn't think you could spur out of a socket as many times as you can fit the cables into the terminal, doesn't sound like the right thing to do even if not in regs.