That's true about the whole RFC they are only 2 legs unlimited skts within permitted square meterage and one sper permitted to each , if those skts are deemed to be likely to supply a heafty loading surley the installation design is at fault and not RFC witch 9/10 will serve occupants more than adequately
 
BS7671 433.1.103 and appendix 15 page 425 (you have got one of these, haven't you?).

very self explanatory. Unfused spur = 1 cable + 1 single gang or 1 two gang socket.
Doesn't say you can't have 2 spurs from the same point. Selection and erection criteria will apply though.
If extending the ring be very careful you don't create a figure of 8!
 
BS7671 433.1.103 and appendix 15 page 425 (you have got one of these, haven't you?).

very self explanatory. Unfused spur = 1 cable + 1 single gang or 1 two gang socket.
Doesn't say you can't have 2 spurs from the same point. Selection and erection criteria will apply though.
If extending the ring be very careful you don't create a figure of 8!

doesn't seem very good practice though even if it is technically allowed.i've only ever come across it in BIY (bodge it yourself!) situations
 
personally I think unfused spur in 2.5mm to a 2 gang is poor practice. Why not use 4mm?
 
personally I think unfused spur in 2.5mm to a 2 gang is poor practice. Why not use 4mm?

funny you should mention that. i was thinking along the same lines. it's like a reverse lollipop circuit. in effect the 4mm would give you a 32A capability on the spur, so theoretically you could add more than 1 outlet on the spur.
 
[/QUOTE] in effect the 4mm would give you a 32A capability on the spur, so theoretically you could add more than 1 outlet on the spur.[/QUOTE]

Then you would be in departure from BS7671 and lots of onus on you to show equivalent safety. Agree this is possible though.

I work on 2x13 A load continuous, 4mm should be good provided installed correctly, i.e. no serious down ratting factors applied. Now totally safe and no chance of thermal overload. I do not like cable rated below breaker rating in ANY situation.
 
I work on 2x13 A load continuous, 4mm should be good provided installed correctly, i.e. no serious down ratting factors applied. Now totally safe and no chance of thermal overload. I do not like cable rated below breaker rating in ANY situation.

In theory it is limited by the fuses in the plugs that will go in the socket. In practice this sort of doesn't work because of unfused doublers etc.

A good example of where fusing down after a reduction in cable size does work is the old busbar chamber method. Tap off in smaller cables and switch fuse after the reduction. Just because the fuse is not immediately before cable reduction does not mean it's not protected.
 
Doing an EICR on a property and came to the kitchen, when i dropped the sockets my jaw also dropped, no end to end on the ring, one socket had the following spurred off of it - 3 double sockets, extractor hood, cooker ignition which then also had another socket spurred off that to feed a washing machine!!!! dropped another socket as looking for other leg of the ring to find a socket fed in 1.5mm!!! The guy has just had his kitchen fitted, looks all lovely and nice on the surface but really bad underneith. This was done by a Romanian builder who has no clue re electrics. I told the guy this needs to be sorted asap, i suggested he'll need a few fcus for the various spurs but it'll mean breaking a tile or two to put them in, cant really put any sockets below as cupboards already fitted, then try to find the other leg and put links between to make a complete ring, cant see any other way of doing it other then putting it on a 20A radial but that's not an ideal solution in my mind really, any other ideas? I thought you could only spur once off a socket unless you put an fcu then you can have as many as you like, didn't think you could spur out of a socket as many times as you can fit the cables into the terminal, doesn't sound like the right thing to do even if not in regs.
 
funny you should mention that. i was thinking along the same lines. it's like a reverse lollipop circuit. in effect the 4mm would give you a 32A capability on the spur, so theoretically you could add more than 1 outlet on the spur.
where does 32A come from?
 
the 4mm on the spur can handle 32A, similar to 2 x 2.5mm if the rfc was extended. whereas a single 2.5mm is only good for 27A (clipped direct).
 
Not in the last regs though as the poster suggested. Daz
could have been thinking of socket fed from fcu and is actually still permitted in that circumstance. also can spur off a spur on a radial circuit, without fcu but only with 20A protection
 
I was taught in college you could only take one spur off any point of the ring. Fine to fuse down to 13A then have as many sockets in a radial spur as you want, but only ONE spur per ring socket.

Now after being taught that I always took it as gospel that it was a reg, although i've never looked it up.
But having read the above posts i'm wandering if my tutor was right or not?
 
I was taught in college you could only take one spur off any point of the ring. Fine to fuse down to 13A then have as many sockets in a radial spur as you want, but only ONE spur per ring socket.

Now after being taught that I always took it as gospel that it was a reg, although i've never looked it up.
But having read the above posts i'm wandering if my tutor was right or not?

it's 1 outlet on an unfused spur off the ring, but if it's a fused spur, you can fit as many as you want.( within reason). see app. 15. bgb.
 