But if the 12v is run in normal twin and earth (i.e. insulated to 230v) then it is acceptable. Yes?

NO!!.....


There is no way that a DP switch can have 2 different voltages on it from 2 different systems. That's just asking for trouble, pure lunacy!!!
 
Last edited by a moderator:
Its for a bathroom light which brings on a fan as well . Not my design, comes from the architect/electrical engineer, who have insisted on a low voltage fan.

I know it is strange but have been told to do it
 
Last edited by a moderator:
No electrical engineer is going to design a system where a single DP switch is going to be used to control 2 systems on different voltage bands... Talk to the guy face to face and not via an arty farty Architect, who is mainly only interested in what it looks like!! I'd want a signed written and dated instruction before i would touch it!!

It's YOU that will be signing your work off, and i can assure you, this set-up does not conform in any way shape or form to BS7671, on segregation of extra low voltage bands, switching, or anything else come to that!!
 
Hi crosswire,

Its for a bathroom light which brings on a fan as well . Not my design, comes from the architect/electrical engineer, who have insisted on a low voltage fan.

Presumably your Extra Low Voltage fan is supplied from a SELV source ?
In which case can you not supply the ELV primary source (the 230V AC incoming supply) from the DP switch, as this will then sort all of your problems wrt mixed supplies ?

Just a thought

Edit, or better still from a DP SW FCU suitably fused down (@ 3A)
 
Last edited:
A question, .... Where are the neutral/return conductors for these 2 systems?? Have they been brought to this switch back box too??

This switch would need so many different warning stickers on it, this Architect will probably end up having a heart attack. lol!!!
 
Hi crosswire,



Presumably your Extra Low Voltage fan is supplied from a SELV source ?
In which case can you not supply the ELV primary source (the 230V AC incoming supply) from the DP switch, as this will then sort all of your problems wrt mixed supplies ?

Just a thought

Edit, or better still from a DP SW FCU suitably fused down (@ 3A)


This is how I would do it , as it is a much more sensible way to go about things. However I am merely a lowly installation electrician and have no input into the design process.

I just wanted to find a Reg that would support me if I chose to argue the point. However reading 528.1 I see that it does NOT forbid such an arrangement:

"EXCEPT where one of the following methods is adopted, neither a voltage Band 1 or a voltage band 2 circuit shall be contained in the same wiring system.......

i) Every cable or conductor is insulated for the highest voltage present"


Which it would be.......so it seems it is ok after all.
 
A question, .... Where are the neutral/return conductors for these 2 systems?? Have they been brought to this switch back box too??

This switch would need so many different warning stickers on it, this Architect will probably end up having a heart attack. lol!!!


The neutral of the 230v system is joined in the back box.

The 12v cable is just a switch line, so no neutral present.

Furthermore, after reading 514.10 there no requirement for warning notices, unless the voltage EXCEEDS 230v, which it doesn't.
So it seems I have no Reg to back me up, should I choose to dispute this arrangement. :(
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
2 voltage bands, 1 double pole switch. Yes or No?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
16
Unsolved
--

Advert

Thread statistics

Created
Crosswire,
Last reply from
GLENNSPARK,
Replies
16
Views
3,723

Advert

Back
Top