im about to go down london to do a job. currently waiting on manweb to install the new cable going in + meter. they have put 100a fuse for a building with 3 story's + basement and all completely home automated "littrally everything is home automated lol" The isolater is roughly 8 meters away from the ccu location and i have a 25mm armored to connect from the isolator to the ccu

Has anyone got the cut outsize for a 3 core 25mm armored cable + im sure there is a regulation on cable the distance apart from the isolator to the ccu? or have i confused my self?

Also anyone installed control 4 home automation. what do use think ? recommendations
 
I am not quite sure what you are actually asking.
The outside diameter of a 3C 25mm² SWA would be about 25mm, if that is what you mean.
A cable run from an isolator to a CU can be of any distance so long as the regulatory requirements are complied with.
The cable run from the origin of a supply to the next protective device should generally be <=3m, but is subject to the DNO's specification.
I have not installed control4home automation so cannot help there. (apart from thinking it is a tremendous waste of money!)
 
as far as i know its just an isolator
Meter tails should be as short as possible. Different metering companies have different policies but the length should always be less than 3 metres of cable from the cut-out through the metering equipment to the consumer unit. If the consumer unit is required to be further away, then a switch and distribution circuit should be installed.
 
so i need to get a switch fuse to be installed? do manweb supply this? or do i have too? and how come as the main fuses are in place?
 
so i need to get a switch fuse to be installed? do manweb supply this? or do i have too? and how come as the main fuses are in place?

You would install the switch fuse. The main fuse is there to protect the DNO's cables/equipment and not to offer over current protection to a consumers distribution circuit.
 
jesus abit costy!! o.o thanks for the link btw il just pop one in tomorrow :) btw you wouldnt know the cut out size for the gland to gointo the board so i can get a cutter?
 
jesus abit costy!! o.o thanks for the link btw il just pop one in tomorrow :) btw you wouldnt know the cut out size for the gland to gointo the board so i can get a cutter?

£59 inc VAT from Edwards. I get them cheaper from my wholesaler but I by a lot each year.
 
jesus abit costy!! o.o thanks for the link btw il just pop one in tomorrow :) btw you wouldnt know the cut out size for the gland to gointo the board so i can get a cutter?

I now really only ever buy starrett CSC smooth cutting holesaws...I would recommend them if your going to buy a cutter as they really are a good bit of kit.
 
Last edited by a moderator:
jesus abit costy!! o.o thanks for the link btw il just pop one in tomorrow :) btw you wouldnt know the cut out size for the gland to gointo the board so i can get a cutter?

Really - surely you included this in your costings before you submitted a price!
 
so i need to get a switch fuse to be installed? do manweb supply this? or do i have too? and how come as the main fuses are in place?

Why not ask the qualified electrician who designed the installation/is signing off the work? Their decision on this is what you need to work to
 
there electrical designer has none of this planned! kind of annoying tbh ive taken on a half completed job so its been abit of a pain in the @@@....
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
25mm Armour installation + home automation "control 4"
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Mike Blair,
Last reply from
Mike Blair,
Replies
19
Views
3,225

Advert

Back
Top