newfutile

-
Arms
Supporter
Does anyone know what size cable to use for a MCG type 2 SPD (3 phase) and what MCB.the manufacturers instructions don’t state any values!

also should i use 3 x single phase or a 3 phase MCB?
 
If it is anything like this one then 32-63A MCB:
There might be some figured in the new regs on SPD cable sizes but I don't have copies of any with me. I would probably look at 10mm as a typical value to go with.

Generally for good SPD performance you want minimum inductance, so C or D curve MCB if you can get them as well as short cables and cables all close together to keep loop area down.

Some of the smaller ones say 16-32A MCB so maybe 32A D-curve is a choice for all. I would go 3P as if you want to isolate for test you would want all poles off!
 
That’s the exact one but in a metal enclosure, it seems a bit vague on sizes. I will see if i can get 5 x 10mm cables though the bushing, it will be installed touching the top of the 3PH DB with cables just long enough to connect .
thanks for the advice.
 
Just looked at 534.4.10 which has the CPC minimum size as 6mm for type 2, or 16mm for type 1 SPDs.

For the live conductor it has to be rated at prospective fault current (so I guess adiabatic for protection MCB) and also minimum of 6mm for type 1 and 2.5mm for type 2 SPD.

So in your case if you have 6mm cable then probably that will do all and neatly as data sheet shows it is OK.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
-
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
3 phase SPD MCB size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
newfutile,
Last reply from
pc1966,
Replies
4
Views
3,863

Advert

Back
Top