Can any one tell me if i need to put rcd on 3036 cu if I am just changing socket faces cause i was told i did?
Last edited by a moderator:
If your supply fuse is a BS1361 and your installation is domestic single phase then you can use the s/c capacity of that device (16.5kA).
not that its important for this post but i thought a 1361 was 33Ka
1361 type 2 is 33ka 1361 type 1 is 16.5 ka
looking at the pics though the discolouration of the fuse carrier is due to the fuse blowing and not to overload , meter tails look like 16 mm ,and if im not mistaken the fuse carrier is a 3036 rewireable , if i am mistaken and i could be then the fuse may will be a BS88 or a 1361 , think ive mentioned them all , but id be suprised if the fuse was any higher than a 60 amp , have a close look at the fuse carrier it may well give you the fuse rating (capacity) on it
anyone else confirm 4ka is the rating for 3036 fuses?
if not and its 1ka for the 5a lighting for example does it not matter that my PFC is greater than this cappacity?
First photo shows main earth attached to incomer with bonding clamp, reckon that's a code 2 on PIR
Yep seen that, heard you loud and clear..
But i dont think i have a 1361 main fuse..
and i always see this ka rating 1 to 4 on 3036 fuses but which is it... 1,2,3 or 4?
Providing earth loop complies with 41B1 in BS 7671 then you don't need an RCCD.