Discuss 80 volts on earth conductor in the Australia area at ElectriciansForums.net

If its a TNCS supply it could be a neutral fault , the path from the neytral is broken and the returns back up the earth to the cdu , are you getting shocks off any metal appliances , or the simpler thing is you have no earth connection at some point ,as lenny has said where are you getting the 80 volts
 
Hi jimra56,

I came across the same problem and traced it a damp area around the socket behind the washing machine, water had been leaking from machine and soaked the wall and the socket was badly installed. Was called to house because owner was getting shocked when she was around her machine.
 
As per Lenny where are you measuring each from, i.e where is you meter connected to the earth point and where is it connected to the neutral? You may have a fault similar to what I experienced.........
I had an interesting fault the other week whilst checking that Class 1 metal socket fronts were earthed. Admittedly it would have been best to carry out whilst dead, however this was just a quick check for peace of mind after doing a different job at night. I found 50v between the metallic light switch front and the main earth terminal at the consumer unit. When the light switch was switched on there was 100v. Further examination showed that the CPC (Earth) to the light switch was disconnected in the ceiling rose. Tests of the earth at the rose proved ok, IR tests on the switch cable proved ok. Reconnection of the CPC (earth) eliminated the problem. All I can put this down to is induction from the live conductors to the CPC conductor. One to look out for though!!
 

Reply to 80 volts on earth conductor in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
476
So, I was messing around yesterday with some old testers I have laying around to see if they still work I found my dads old Robin MFT and noticed...
Replies
8
Views
541
Hello folks, So my van got found after being stolen ;D Now I'm installing my own alarm on the van which is triggered when a door is opened. Im...
Replies
4
Views
519
HI everyone I'm getting 255 volts between live and earth natural to live on a live lighting circuit fed from 6amp rcbo , When switch off I'm...
Replies
1
Views
860
hi all, i have a problem of over charging on my 65 s type jag. i changed the voltage regulator for a new after market one same as what was on the...
Replies
16
Views
934

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock