Hello fellows,

Just wanted to get your thoughts on this...

I'm working on a property with a TT supply in the hills, I have tested the Ze at 13.5 Ohms, very healthy Earth Rod I thought. Only problem is that its been concreted over through the years so all that now exists is the earth cable with mechanical protection running into concrete outside. No sign of an earth rod anymore as its underground.

Id love to get your thoughts and the regs on this, and whether I should be putting in a new earthing rod or passing this one as its safe and sound underground, encased in concrete.

What do you think?

Daniel
 
Does anyone know for certain that it is connected to an earth rod and not, for instance, a metal utility pipe. Also you are unable to see the quality of the connection so i would think there is a case to be made for putting another rod in, or at least one in parallel - Maybe a code 3 further investigation???
 
Hello fellows,

Just wanted to get your thoughts on this...

I'm working on a property with a TT supply in the hills, I have tested the Ze at 13.5 Ohms, very healthy Earth Rod I thought. Only problem is that its been concreted over through the years so all that now exists is the earth cable with mechanical protection running into concrete outside. No sign of an earth rod anymore as its underground.

Id love to get your thoughts and the regs on this, and whether I should be putting in a new earthing rod or passing this one as its safe and sound underground, encased in concrete.

What do you think?

Daniel
if rod is unaccesible for inspection and maitenance then it does not comply with the requirements of BS 7671 i would install a new rod
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Access To TT systems Earth Rod for PIR?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
ThomasElectric,
Last reply from
fulla,
Replies
2
Views
2,236

Advert

Back
Top