Well yes it was running not cutting anything and it was pulling 16a per phase the saw has been getting used for years in another building so the 5 core 2.5mm cable that came with saw has been ok in previous building would you be happy to leave it on c type 50 a breaker or am I worrying to much lol

It will jump up once its under load my friend, the saw's just spinning freely there...


Likely not 50A but still...
 
May I ask what type of saw and who manufactures it? If you can find the Manual it should almost certainly have the Kva described, from there work out the Amps that it converts to. But Brightspark is correct, and I also agree that it's probably not 50A. Recently installed a derelict kasto horizontal band saw and it only pulled 12.7A under load. But I would check and not just assume from your clamp meter, use the manufacturers rating.
 
If your really worried, what's the cable run length ? How's it grouped? do your calcs, then you will know all you need to know, then clamp saw under full load.
It will be fine as is I'd say, but it makes for good practice for you to do the calcs.
 
Farm be very careful i can almost guarantee the advice you gave was incorrect and you would have seen it tripping on start-up had you fitted a 20a (c) or (d)... You need the Kw or Hp of the motor first (im assuming this is DOL or star/delta start up), the motor rating will determine the mcb rating which lastly give you the cable size..... too many people do this the college taught way for a standard resistive load but we are looking at high inductive loads which need to be worked out in a different manor.... i suspect the set-up as is could be problematic if the motor is higher than 9kw which i suspect it is if its idoling at 16amps.

Get the Kw rating and il give you your options with this existing set-up.....

Ps i fit motors and machines for a living mostly bigger beasts than small workshop ones usually 37kw, 45kw also not knowing the actual actions of the saw will this ever start under load or as i suspect be loaded after reaching full speed.
 
Last edited by a moderator:
Dark wood there's no plate on saw telling me anything just a 5 core 2.5mm cable already connected into saw I've just connected this to my isolator and carried out my dead and live test
 
So you have a potential of pulling 50 amps through the manufacturers 2.5mm phases? And 5-6 times that at start up as its a c type?
 
So you have a potential of pulling 50 amps through the manufacturers 2.5mm phases? And 5-6 times that at start up as its a c type?

Your forgetting the motor will have motor O/L protection the 2.5 are not been protected from overload by the front end only from S/C

And Farm you could always look at the overload setting , if DOL then rough trick if assume its set to FLC is to half this value for Kw rating ...if star delta then depends what position the O/L is in to whether it derated to 0.58 of Flc in which case just rough guess this setting as kw rating .... although you wont be spot on it gives an idea.

A 7.5kw or 9.33kw motor will not nuisance trip a 50(c) on a typical machine, anything over this starts to get into the nuisance tripping on start-up but type (d) can mean reducing mcb size if ELI complies and could see larger motor fitted upto 22kw depending on duty and run-up time (50A-type D) can allow this.
 
Sorry just re-read you post and see Progressing's angle (silly name by the way hard to point you out in a sentence without confusion), thought you meant motor connections were 2.5mm but you mean the supply cable to machine well again not the norm' as you usually keep the supply to the same size to the machine but you could argue the issue here as it has upfront limiting current device thus derating of cable size could be permitted depending on your interpretation of reg 433.2.2
 
Last edited by a moderator:
yes the cable is the manufactors glanded into a conduit through box mounted on the saw cables go into a connector its 3 phase n and e and even the internal cables are all 2.5mm the saw is pulling 16a per phase on full load but will clamp again today the supply cable of 4 core 10mm is a cable that was used for another machine previously so even though its on a ctype 50a breaker it will never pull that
 
With all due respect farm the costing should have be done prior to the job including any derating of mcb, if customer complains about quote then you dont do job, if you have just gone ahed connected machine then said it needs derating at £--- amount for the part then your in a corner as you need to ensure your jobs correct yet try keep your customer happy, if you check the control box in the saw it may or should have fusing down for control circuits etc and of course O/L protection of motor, and even though the existing is 2.5mm supply loom to controls it dosn't mean its correct - as the installer of the new supply to the machine you really should be gauging whether the existing supply loom was correct. It may be the case it was on HRC fuses motor rated which can allow for the 2.5mm cables but because you putting it on a mcb then you have to avoid nuisence tripping which can increase the size of mcb and also cable size.... now you already have 10mm so why not just extend the 10mm to include the supply loom to the machine. If the machine is brand new then follow the instructions guidelines... if i suspect it 2nd hand then you have to forget how it came and design the supply yourself.
75% of the machines 2nd hand that i do are incorrectly installed previously, even had a full factory of solder bath units wired in 25mm swa on 80amp mcbs when 10mm on 40amp supplys would have sufficed all because their resident sparkie hadn't converted the American plates 3ph at 220v to our british 3ph 400v even though he'd fitted transformers to convert supply.
 
yes the cable is the manufactors glanded into a conduit through box mounted on the saw cables go into a connector its 3 phase n and e and even the internal cables are all 2.5mm the saw is pulling 16a per phase on full load but will clamp again today the supply cable of 4 core 10mm is a cable that was used for another machine previously so even though its on a ctype 50a breaker it will never pull that

If the saw wasnt cutting like you said previously then it isnt full load...current will vary depending on whats being cut too...
 