With all due respect farm the costing should have be done prior to the job including any derating of mcb, if customer complains about quote then you dont do job, if you have just gone ahed connected machine then said it needs derating at £--- amount for the part then your in a corner as you need to ensure your jobs correct yet try keep your customer happy, if you check the control box in the saw it may or should have fusing down for control circuits etc and of course O/L protection of motor, and even though the existing is 2.5mm supply loom to controls it dosn't mean its correct - as the installer of the new supply to the machine you really should be gauging whether the existing supply loom was correct. It may be the case it was on HRC fuses motor rated which can allow for the 2.5mm cables but because you putting it on a mcb then you have to avoid nuisence tripping which can increase the size of mcb and also cable size.... now you already have 10mm so why not just extend the 10mm to include the supply loom to the machine. If the machine is brand new then follow the instructions guidelines... if i suspect it 2nd hand then you have to forget how it came and design the supply yourself.
75% of the machines 2nd hand that i do are incorrectly installed previously, even had a full factory of solder bath units wired in 25mm swa on 80amp mcbs when 10mm on 40amp supplys would have sufficed all because their resident sparkie hadn't converted the American plates 3ph at 220v to our british 3ph 400v even though he'd fitted transformers to convert supply.