I’m
An NICEIC DI.
I haven’t got around to doing my 18th yet and I haven’t got the new literature.
How do you determine if you need to fit an SPD board.
Should I start fitting these on all my jobs now?
 

Matthewd29

-
Arms
Esteemed
Assess the need for it. Very rare in domestic households. I havnt fitted one yet to be honest there is absolutely no requirement to do so
 

Midwest

-
Arms
Esteemed
Not done the 18th, and currently not working as a spark.

However, I've read some posts on here about this subject, and I believe the regs suggest a risk assessment for SP in domestic dwellings; one bit of which is property value, around a few thousand pounds?

Telly's, fridge freezer, washing machine, etc etc, soon adds up. Not that I'm aware of being subjected to any 'surges'.
 

Wilko

-
Arms
Esteemed
Hi - for single domestic dwellings - I mention them to Customer and explain the benefits and the cost. I follow their direction and record on EIC. Some are happy to invest :) .
 
N

Nigel

Still sparks giving false or bad advice on these.

SPDs can only be omitted in single dwellings ‘where the total value of the installation and equipment therein does not justify such protection’.

443.4 refers and uses the term ‘shall be installed’. Basically if the installation has electrical equipment over the value of about £200 BS 7671 states SPDs shall be installed.
 
Still sparks giving false or bad advice on these.

SPDs can only be omitted in single dwellings ‘where the total value of the installation and equipment therein does not justify such protection’.

443.4 refers and uses the term ‘shall be installed’. Basically if the installation has electrical equipment over the value of about £200 BS 7671 states SPDs shall be installed.
Errr... agreed... alot of bad advice...

443.4 actually says that there are 4 specific situations when you must fit an SPD (I won't type them out here, but this does not include my house).... OR you do a risk assessment... IF no risk assessment, you fit one anyway (i.e. you assume the highest risk)

So for my house, it's not one of the specific situations, so I've done a risk assessment and the 'Calculated Risk Level' is >1000... therefore No SPD is required.
 
N

Nigel

Errr... agreed... alot of bad advice...

443.4 actually says that there are 4 specific situations when you must fit an SPD (I won't type them out here, but this does not include my house).... OR you do a risk assessment... IF no risk assessment, you fit one anyway (i.e. you assume the highest risk)

So for my house, it's not one of the specific situations, so I've done a risk assessment and the 'Calculated Risk Level' is >1000... therefore No SPD is required.
The risk assessment is not required for single dwellings so there really was no need to do one. This is clearly stated in 443.4 and then goes on to state what I have said above.

As I said. In a single dwelling there is no requirement to carry out a risk assessment and SPDs shall be installed of the value of electrical equipment is over about £200.

Can you show me your calculations please that say SPDs are not required on your dwelling?
 
The risk assessment is not required for single dwellings so there really was no need to do one. This is clearly stated in 443.4 and then goes on to state what I have said above.

As I said. In a single dwelling there is no requirement to carry out a risk assessment and SPDs shall be installed of the value of electrical equipment is over about £200.

Can you show me your calculations please that say SPDs are not required on your dwelling?
I think the issue is with the way that Paragraph 2 of 443.4 is read... you're correct in saying that there is no requirement to carry out a risk assessment... but, if you don't do one, then you should install SPD, unless it's a single dwelling and the value of any potential loss is small (your £200 figure)... if that makes sense.

As to the calculation... Example 4 on Page 106 of the 18th is exactly my situation... so it's all detailed there... This shows my CRL is 1,700 which is higher than 1,000 so no SPD is required.
 

happyhippydad

-
Arms
Esteemed
As you can see from above the answer is clear.
Maybe you should or shouldnt consider an SPD but probably not or perhaps sometimes, unless otherwise indicated.
As usual the regs are clear and transparent.
I can't see where the confusion lies?
 

Ian1981

-
Mentor
Arms
Esteemed
6339BEB2-3DE0-4DCB-8996-EB39CDB32920.png This is Beama’s guidance on the matter taken from BSEN 60363-4-44
Certainly on the recent webinar I watched by the NICEIC and by my recent assessment, there does not seem a requirement to mandatory install one in a domestic dwelling in their eyes at least, but it should be advised to the customer the benefits of such protection.
Of course indent 1 loss of life could come under a domestic dwelling if there’s life affecting medical equipment located inside
 
Last edited:

Strima

-
Arms
Esteemed
The cost of SPDs will get lower and get to such a point that their addition to an installation will become the norm.

Give your customers the details and let them make an informed decision.
 

Andy78

-
Mentor
Arms
Esteemed
The cost of SPDs will get lower and get to such a point that their addition to an installation will become the norm.

Give your customers the details and let them make an informed decision.
They are already pretty cheap. SBS has them listed at £20 on his
current price list.
 
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members

Reply to Advice needed On 18th edition boards. When do fit SPD boards? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Top Bottom