Discuss AFDD in 18th 2nd Amendment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Status
Not open for further replies.
Same
You cannot explain why you think this. A bit of a know-it-all eh!

Your attitude gets really offensive when you struggle with people who have greater electrical knowledge than you. I remember some of your previous threads went the same way.

Keep it civil and a good discussion can be had.
 
531.3.2
(iii) in order to avoid unwanted tripping by protective conductor currents and/or earth leakage currents, the accumulation of such currents downstream
of the RCD shall not be more than 30% of the rated residual operating current.


And?
And your proposed appliances tot up to?
 
I the design does not conform to the 18th with amendments, then he can tell us where.
So far no has. All I have read is innane circular babble though. Now back to watching the football.
Yes it is yours you have not answered any question that has been posted so far and have only chosen to respond with condescending comments about other peoples knowledge of the subject
So can we have some answers to the questions that have been asked in a coherrent manor
 
Will you drop the sharpen up there is absolutely no need for it in a civilised conversation and it really makes you sound like a bully

The point of this group is for discussion just because someone doesn't agree with you there is no need to belittle them when they present an alternative point of view

You are certainly living up to your profile of Manufacturer / Distributor / Supplier / Inventor - etc and in this thread you have met all four of the areas you operate in
Don't forget, he's also a Tech Writer
 
It is not a novel to read while in bed.
It's not a novel, but I suggest you should read it, whether in bed or not.

But there again you may drive yourself mad, as there maybe so much that you don't agree with or don't understand.
 
And your proposed appliances tot up to?
As all the heavy appliance are not on the final ring, well a TV, charging the laptop occasionally, fridge, maybe the occasional use of an electric kettle (kettle can go on the hob), and a vacuum cleaner used a few minues per day. Big load on a 32A final ring eh? ;)
 
It's not a novel, but I suggest you should read it, whether in bed or not.

But there again you may drive yourself mad, as there maybe so much that you don't agree with or don't understand.
Tell me where it does not conform to the 18th and its amendments? Round and round again. I will be waiting a loooooong time!
 
Again, tell me where it does not conform to the 18th and its amendments? Round and round again.
You have been asked questions by a number of posters and you continue with your inane comments without answering the questions asked
It is you who continues to drive this thread round and round as you seem unable or have an inability to answer fairly simple questions that members have posted regarding your hypothetical minimalist installation
 
As all the heavy appliance are not on the final ring, well a TV, charging the laptop occasionally, fridge, maybe the occasional use of an electric kettle (kettle can go on the hob), and a vacuum cleaner used a few minues per day. Big load on a 32A final ring eh? ;)
Nope you are not understanding the question in relation to Regulation 531.3.2(iii). Do you not understand it?
 
Nope you are not understanding the question in relation to Regulation 531.3.2(iii). Do you not understand it?
If you read, and understood, this thread you will know I do. Earth leakage by plug in appliances. ;) I posted 531.3.2(iii), which the poster who brought up 531.3.2(iii). up never did.

The exercise circuit is sound and conforms to the 18th and amendments.
 
Last edited:
  • Funny
Reactions: UNG
If you read, and understood, this thread you will know I do. Earth leakage by plug in appliances. ;) I posted 531.3.2(iii), which the poster who brought up 531.3.2(iii). up never did.

The exercise circuit is sound and conforms to the 198h and amendments.
So the combined leakage will not exceed 9ma.
 
Why don't you answer the question instead of just throwing things back all the time?
I am not the one bringing it up. so. Are you saying it will? If so, explain.

The excercise design conforms to the 18th and amendments.
 
I am not the one bringing it up. so. Are you saying it will? If so, explain.

The excercise design conforms to the 18th and amendments.

What leakage current would you expect in your design?
 
Status
Not open for further replies.

Reply to AFDD in 18th 2nd Amendment in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Locked
So, a flat 6 floors and above needs an AFDD on each socket circuit. At up to £150 each it is going to be an expensive undertaking if there are...
Replies
21
Views
3K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock